Hi guys just finishing off a rewire where I have a 6mm 3 core SWA Sub main running to an outbuilding. I'm connecting into a 10 way plastic cu in the house which is going to be positioned just under the ceiling in the hallway with the cable dropping down from above into it. Just wondered on the best way to connect the SWA I've heard people mention earthing nuts but never come across them. It is a T-N-CS earthing arrangement and is going on a 40a MCB, non RCD, protected running to a metal clad board in the outbuilding with the 3rd core used as the cpc and armour connected on the supply end. Any advice would be appreciated :)
 
Really?

You do much comerical/industrial?

a lot of designers spec cpc's in conduit now a day's.

Search in google for 20mm earth coupler and it be one of the first pics

I do a bit of conduit work and always use use the conduit as CPC when the calculations allow (which has been always so far)
I am aware that designers do like to waste miles of copper like that yes, I guess it just proves they like to go for the easy life rather than designing properly. Guidance note 8 is pretty clear on the subject when it says that adding a cpc in steel conduit is a futile exercise.

I can honestly say i've never seen a coupler like that before, and it looks a bit ridiculous to me.
 
Guidance note 8 is pretty clear on the subject when it says that adding a cpc in steel conduit is a futile exercise
I had an argument at work last week with the senior spark on the job.
2 steel boxes joined with a bush and couplers, I didn't link the 2 with a bit of copper. He said I was wrong, he also said that the NIC man wants it done his way. I told him the NIC man was a dick who didn't know what he was doing (also implying the same about him)
We juiced up the circuit and took Zs readings, there was no difference.
Me 1, him and the NIC man 0
 
I had an argument at work last week with the senior spark on the job.
2 steel boxes joined with a bush and couplers, I didn't link the 2 with a bit of copper. He said I was wrong, he also said that the NIC man wants it done his way. I told him the NIC man was a dick who didn't know what he was doing (also implying the same about him)
We juiced up the circuit and took Zs readings, there was no difference.
Me 1, him and the NIC man 0

This is why I hate the NIC,

Not in the NIC, follow BS7671

In the NIC, follow BS7671 + some idiotic rules they think up!
 
Why's that mate? I realise that there's a belt and braces argument but if the conduit is mechanically and electrically sound and disconnection times are going to be met it seems like a waste of cable

True but around birmingham a lot of the sparks dont bother to tighten things up.

Everything is finger loose as one of them like to say:D

You can undo it with 1 finger:D
 
They want sacking then and they need to get someone in to do a proper job

Finger loose what a load of ---- that is

The whole job was a fk up.

3 floors.

Ground, first,second and roof plantroom

Different firm for pipefitters,electricians etc on each floor.

The ground were house bashers and the firms from first and second had to help them to get it done on time
 
Why's that mate? I realise that there's a belt and braces argument but if the conduit is mechanically and electrically sound and disconnection times are going to be met it seems like a waste of cable

more like "is a waste"

reminds me of just the other day when i went round after someone who said they`d carried out a visual and `identified` the installation had no R2....

ex council house...
so you know what i was going to say next dont you....
 
Why's that mate? I realise that there's a belt and braces argument but if the conduit is mechanically and electrically sound and disconnection times are going to be met it seems like a waste of cable

Hi Trev, yeah all the work we done was for local authority, Hospitals,schools when GLC run the show.!!, and it was in the spec, in fact it's never been a situation for me not to provide an cpc in conduit, weather it be black enamel or galvo, still can't see me having ever to thread or set again. lol
 

Reply to SWA into plastic cu in the UK Electrical Forum area at ElectriciansForums.net

Similar threads

totally agree
Replies
12
Views
892
  • Question
All the lamp post cutouts I've ever seen have a twin swa gland plate built in to the base.
Replies
2
Views
615
loz2754
L

Recommended Sponsor News

Exclusive Forum Offer! Free euro 2024 wall chart for first 10 responses!

Hi everyone,

We have 10 exclusive Uheat EURO 2024 Wallcharts to giveaway for Electricians Forum Members! The first 10 people to reply YES to this thread - I will message and get them sent out to you just in time for this years tournament! GO GO GO

Quickwire Now Sponsor ElectriciansForums.net

I am sure you will join me in welcoming our newest sponsors of ElectriciansForums.net - Quickwire! They have decided to join us after seeing you guys discussing their products here. Now we have an expert on board that you can chat to @Quickwire-Sam who will be happy to answer your queries!

[ElectriciansForums.net] Quickwire Now Sponsor ElectriciansForums.net


@Quickwire-Sam said "At Quickwire, we're all about speed, safety, and reliability. We're a family-run business, and every Quickwire connector is proudly made right here in the UK, ensuring noticeable quality. In short, Quickwire is the fastest connection method on the market. Whether you're an experienced electrician or a DIY enthusiast, Quickwire makes electrical connections ridiculously quick and easy. We're passionate about blending British craftsmanship with innovation. If you have any questions or if there's any way we can help, please just ask me!"

PCBWay Now Sponsor ElectriciansForums.net!!

I hope you will all join me in welcoming our newest sponsor to the forum PCBWay! You can contact their friendly people by sending a message to @PCBWay who will be happy to answer your queries.

Welcome to the community and thanks for your sponsorship!

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

PCBWay provides services including PCB Prototype and batch Production, PCB Assembly (SMT), 3D Printing, CNC Machining, PCB Design, Electronics Modules Selling, etc. We are committed to meeting the needs of global makers from different industries in terms of quality, delivery, cost-effectiveness, and any other demanding requests in electronics.

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top