Hi guys just finishing off a rewire where I have a 6mm 3 core SWA Sub main running to an outbuilding. I'm connecting into a 10 way plastic cu in the house which is going to be positioned just under the ceiling in the hallway with the cable dropping down from above into it. Just wondered on the best way to connect the SWA I've heard people mention earthing nuts but never come across them. It is a T-N-CS earthing arrangement and is going on a 40a MCB, non RCD, protected running to a metal clad board in the outbuilding with the 3rd core used as the cpc and armour connected on the supply end. Any advice would be appreciated :)
 
Gland the swa into the CU, where you fit the banjo drill through and drop a bolt into the hole. After you fit washers and a nut or 2 crimp a lug onto an appropriately sized fly lead and take that to the earth bar with the third core.
Btw, if you're fitting a CU up against a ceiling you need a rethink.
 
You will need to earth the armour properly at the other end too as the gland in to the metal board there will give a partial connection even if you don't intend it to.
At the supply end I would probably gland it into a galv through box and then bush that to the CU. That gives you good mechanical fixing of the SWA to prevent it bending your CU out of shape and a handy earth terminal to bond the armour.

If you search for pirannah earthing nuts you will see what you have been missing out on there.
 
Or gland into the board and use 1 of these
 

Attachments

  • image.jpg
    image.jpg
    12.6 KB · Views: 294
Yeah this is the problem with the position of the board. I may have to consider placing a box as suggested to the side of the cu, gland into that and take the cores through the side. Any thoughts on this?
 
If you are installing a 6mm swa (I take it there is nothing extraneous in the 'outbuilding' ?) then it shouldn't stress the CU if you cleat appropriately - I would go with Trev's idea since it's in a hall and appearance may be an issue.
 
As Hawkmoon has indicated if the supply is PME/TNC-S and this outbuilding has any extraneous metalwork/pipes etc, then a 6mm 3 core isn't going to crack it. It's then going to be either a 10mm 3 core, or running in a separate 10mm earthing conductor alongside the 6mm SWA...
 
Yeah this is the problem with the position of the board. I may have to consider placing a box as suggested to the side of the cu, gland into that and take the cores through the side. Any thoughts on this?

Yes, I go with this option. Either a galv adaptable box or a right angle galv conduit box. Either would give a solid connection and look neat.
 
So am I right in saying that with these earthing nuts you gland the cable as normal and the earthing but just goes over the thread and is held with the grub screws? Then a fly lead from this to the MET?
 
So am I right in saying that with these earthing nuts you gland the cable as normal and the earthing but just goes over the thread and is held with the grub screws? Then a fly lead from this to the MET?

Yes you just replace the banjo and retaining nut with the piranha nut.
The grub screw prevents the nut from loosening and the screw holds a ring terminal for the earth fly lead.
earth nut in situ.jpg
 
Pic didn't work, I can't say I've ever seen such a thing though, top hats are the only type of coupler I know of with better earth connections.

And what do you mean by in the past? Conduit is still used as the cpc.
 
Pic didn't work, I can't say I've ever seen such a thing though, top hats are the only type of coupler I know of with better earth connections.

And what do you mean by in the past? Conduit is still used as the cpc.

Really?

You do much comerical/industrial?

a lot of designers spec cpc's in conduit now a day's.

Search in google for 20mm earth coupler and it be one of the first pics
 
Really?

You do much comerical/industrial?

a lot of designers spec cpc's in conduit now a day's.

Search in google for 20mm earth coupler and it be one of the first pics

I do a bit of conduit work and always use use the conduit as CPC when the calculations allow (which has been always so far)
I am aware that designers do like to waste miles of copper like that yes, I guess it just proves they like to go for the easy life rather than designing properly. Guidance note 8 is pretty clear on the subject when it says that adding a cpc in steel conduit is a futile exercise.

I can honestly say i've never seen a coupler like that before, and it looks a bit ridiculous to me.
 
Guidance note 8 is pretty clear on the subject when it says that adding a cpc in steel conduit is a futile exercise
I had an argument at work last week with the senior spark on the job.
2 steel boxes joined with a bush and couplers, I didn't link the 2 with a bit of copper. He said I was wrong, he also said that the NIC man wants it done his way. I told him the NIC man was a dick who didn't know what he was doing (also implying the same about him)
We juiced up the circuit and took Zs readings, there was no difference.
Me 1, him and the NIC man 0
 
I had an argument at work last week with the senior spark on the job.
2 steel boxes joined with a bush and couplers, I didn't link the 2 with a bit of copper. He said I was wrong, he also said that the NIC man wants it done his way. I told him the NIC man was a dick who didn't know what he was doing (also implying the same about him)
We juiced up the circuit and took Zs readings, there was no difference.
Me 1, him and the NIC man 0

This is why I hate the NIC,

Not in the NIC, follow BS7671

In the NIC, follow BS7671 + some idiotic rules they think up!
 
Why's that mate? I realise that there's a belt and braces argument but if the conduit is mechanically and electrically sound and disconnection times are going to be met it seems like a waste of cable

Agreed, in fact I'd add, it doesn't just seem like a waste of cable, it is a waste of cable!
 
Why's that mate? I realise that there's a belt and braces argument but if the conduit is mechanically and electrically sound and disconnection times are going to be met it seems like a waste of cable

True but around birmingham a lot of the sparks dont bother to tighten things up.

Everything is finger loose as one of them like to say:D

You can undo it with 1 finger:D
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Truro

Thread Information

Title
SWA into plastic cu
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
45
Unsolved
--

Advert

Thread statistics

Created
longers30,
Last reply from
shanky887614,
Replies
45
Views
5,341

Advert

Back
Top