Hi everyone,

I have a 2 core 10mm2 SWA from a DB to a consumer unit to be joint. I know seems a silly question but how can I joint the steel of the SWA?

Thank you
 
If you have to join cables mid-way then something like this has all the bits you need and is properly waterproof if you follow the instructions precisely:
https://www.cef.co.uk/catalogue/pro...-resin-joint-kit-for-cables-up-to-16mm-2-core

But usually you use the glands at the ends and avoid joints if at all possible.
Thank you. The client wants to use this SWA(it is for temporary use)most likely to save money. However I have missed the green insulated conductor included in the kit which will give the continuity of the steel. Glands will be provided on both side.
 
More importantly, is the armour suitable for using as a cpc for your circuit design?
 
Thank you. The client wants to use this SWA(it is for temporary use)most likely to save money. However I have missed the green insulated conductor included in the kit which will give the continuity of the steel. Glands will be provided on both side.
So the jointing kit is missing the earth link?

10mm 2-core has armour equivalent of 26mm steel = 3.25mm copper approx (6 ohm / km) so you would need some copper braid of roughly 4mm CSA as a replacement. Depending on the space available it might be a case of using 2 * 2.5mm stranded insulated wires, but you would need to be very sure it was making a proper connection when clamped.
 
I am reading the original post as "how do I connect the armour of the SWA to consumer unit, and also to the DB".

Answer - use the proper type and size of gland for the SWA cable, along with the supplied earth connection ring (banjo) bolted through the metalwork using brass bolts and nuts.

Or is it just me?
 
I read the OP as
I have a 2 core 10mm2 SWA from a DB to a consumer unit to be joint.
and with a little imaginative spelling correction i get:

"I have a 2 core 10mm2 SWA from a DB to a Consumer unit to be JOINED"

So I think the suggestion of the torpedo joints with resin is right. Also the copper equivalent of the missing earthing link between the two armours.
 

Reply to SWA joint the steel of a 2 core in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
757
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
976

Similar threads

I am with you. Their RCD did not comply with the standard. The only one I know that does comply, though I am sure it isn't alone, is the Garo...
    • Like
Replies
10
Views
781
  • Question
Better off with the click prw213 as it has twin screw termination.
Replies
9
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top