Hello,

Been to look at job, a barn that's been converted into separate flats. Each one is fed by a 10mm 3C SWA. On peak, off peak and neutral. Currently they just have a double pole main switch for isolation but no protective device. Is there a nice little unit I can use that's designed to deal with something like this? At the moment I thinking of using a 3p&n main switch and then each line on an MCB.

Many Thanks.
 
How about a 3P MCB ?
In principle, you have a setup that can overload the neutral if both peak & off peak supplies are in use - a 3P MCB will protect against that as well as L-E faults on either supply.
 
Hello,

Been to look at job, a barn that's been converted into separate flats. Each one is fed by a 10mm 3C SWA. On peak, off peak and neutral. Currently they just have a double pole main switch for isolation but no protective device. Is there a nice little unit I can use that's designed to deal with something like this? At the moment I thinking of using a 3p&n main switch and then each line on an MCB.

Many Thanks.
What's the earthing arrangement. ?
 
Hello,

Been to look at job, a barn that's been converted into separate flats. Each one is fed by a 10mm 3C SWA. On peak, off peak and neutral. Currently they just have a double pole main switch for isolation but no protective device. Is there a nice little unit I can use that's designed to deal with something like this? At the moment I thinking of using a 3p&n main switch and then each line on an MCB.

Many Thanks.
I take it there's no gas supply obviously but what other main protective bonding conductors are required .
 
Cheers for the replies.

They are shoe box bedsits, 1 storage heater, immersion, cooker, shower.

It's a TNCS

No gas, no oil, plastic water main.

How about a 3P MCB ?
In principle, you have a setup that can overload the neutral if both peak & off peak supplies are in use - a 3P MCB will protect against that as well as L-E faults on either supply.
Thanks, that sounds more tidy than my idea.
 
It seems crazy the shower will be the same size as main supply but I suppose you could have a 16mm t and e feeding 11 kw shower due to the instalation method ,glass wool ,volt drop etc with a 16mm split con and 80 amp fuse at service head and you would think nothing of it
 

Reply to the thread, titled "SWA protection with off peak" which is posted in UK Electrical Forum on Electricians Forums.

Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Daily, weekly or monthly email

Back
Top