Does anyone know the cable size for a 400V 4C SWA/PVC Cable run on galvanised tray for a 250A supply. Is it a 4C 150mm with a 70mm CPC?????
Thanks in advance
Thanks in advance
Discuss Swa/pvc cable size in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
Table 4D4A Multicore 70ºC armoured thermoplastic insulated cables.
Reference method E (in free air or on a perforated cable tray etc, horizontal or vertical).
95mm² cable has a current carrying capacity of 251A. Impedance per meter of 0.43mV.
120mm² cable has a current carrying capacity of 290A. Impedance per meter of 0.35mV.
150mm² cable has a current carrying capacity of 332A. Impedance per meter of 0.29mV.
So long as it is PVC SWA PVC those figures are fine but if it is XLPE SWA PVC then only the 120mm 4 core is suitable with armour being used as cpc 206mm steel which has a copper equivilant of 66.2mm.
Sent from my iPhone using Tapatalk.
700ºC nice.
I couldn't make head nor tail of that table.
I use one produced by a friend from the IEE.
That lists 95mm² 90ºC 4 core as having a CSA of 147mm².
As an aside, there is no way that 206mm² steel has a copper equivelance of 66.2m², more in the region of 26mm².
700ºC nice.
can anybody give us a definitave way of converting steel CSA into equivelant copper?