Not in order to comply with BS7671.Copper equivalent should be used for all bonding regardless of earthing arrangement
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss Swa/pvc cable size in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
Not in order to comply with BS7671.Copper equivalent should be used for all bonding regardless of earthing arrangement
Not in order to comply with BS7671.
Not in order to comply with BS7671.
For TT, and TN-S sytems, there is no requirement for a copper equivalance.
That applies where the bonding conductor is required to have a CSA greater than 25mm².
Anyone got acopy of the John Peckham table? Could do with seeing if thr one I've been given is correct.Chris,
I found this in the Sticky threads on this subject. It is the paper John Shepherd wrote that includes the table that Spin and i use a a good rule of thumb for guidance on the SWA CSA etc....
Using the armour of SWA.pdf
Anyone got acopy of the John Peckham table? Could do with seeing if thr one I've been given is correct.
Got to dabble in some thread necromancy from time to timeWelcome to the forum, Lister
Anyone got acopy of the John Peckham table? Could do with seeing if thr one I've been given is correct.
As I Understand it, this is thr incorrect data and not John's information.Use SWA as CPC, a guide to the acceptability of steel wire armour use as CPC.
SWA as the CPC? In most case it is fine to use the SWA as a CPC.gadsolutions.biz