B

BillyH

What options do i have for terminating a 16mm 3 core swa into a plastic consumer unit?
 
Hi,

You could terminate the swa into a seperate box that you would mount near the cu, then in the box, you would conect it to t&e via choc bloc, terminals etc. Then the t&e would go to the cu.

Cheers

Jay
 
just glandf the SWA into the CU, and then use a banjo, bent at 90deg to allow lug to be attched inside of the CU. This will reduce your Zs, and will take an extra few seconds. its not good practice to introduce joins in a cable, where there will be no need. As for not using a gland, this is also bad practice, unless the accessory is designed for the purpose, eg, some street lights.
 
agree^^^ best not to introduce joints if not necessary. but deffo use a gland. make sure SWA is well supported close to the CU so as not to put a strain on the box around the gland.
 
Try and fit a conduit box to the consumer unit,it can be fixed securely reducing strain on the cons unit and allow the termination of the Swa to be done

that is a good idea by des, and you can still use a banjo if you wish on the bush on the inside of thje CU. If it was a smaller cable, you could use the 4mm lug hole in the back of the box
 
Personally i would never convert a SWA cable to T&E in an adaptable box in this circumstance. If you mount the metal adaptable box directly under the CU enclosure connected via plastic or metal coupling or other, you can then make your SWA termination off with a banjo or earthing nut to the box and take your conductors straight through to the CU, ....Sorted!!


As stated above, introducing unnecessary joints is never a good idea, especially when talking about the larger sized of domestic cables.

I've never seen street lighting with a means of earthing SWA cables without making use of a gland, and can't picture them either. you can't clamp them, without putting undue stress on the internal conductors. If anyone has a link to these accessories, i'd be interested to have a look at them.... Some of the worst corrosion i've seen on SWA cables have been at street lighting positions...
 

Reply to SWA submain into plastic consumer unit? in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
356
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
909
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Sounds more positive.
Replies
8
Views
626

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top