Any suggestions as to how to terminate swa into a switch/fuse neatly? I've run it through a metal box and out to the switch with the switch cover covering the point where the sheath is split but wondering if there's a neater way to do things?
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss SWA to Switch? in the UK Electrical Forum area at ElectriciansForums.net
Would you get two 25mm tails though a single gland?
Are you trying to wind me up. April fools was yesterday
I'm always a bit late...sorry. I'm still on the yellow book ;-)
I'm joking about the book of course, but I have to admit, the last time I looked at one of these books was during my half day 17th update all those years ago
Anyhow, that must be a massive gland to fit two 25mm's through! Surely too big to fit in a 25mm knockout?
How ever you you enter the box with your tails if they are exposed they need to be double insulated and restrained in some manner so any external movement on the cable will not act directly on the terminations... can you not terminate into a 25mm metal through box and bush it to the box running the cores straight through and tapping of the box for earth?
That enclosure will happily take a 38mm gland possibly even a 50mm. I would say you would get 2 x 25mm tails into a 32mm.
Oi Oi Oi ! Clueless... thanks cockney reject