I'm just wondering if anyone knows of a product that can switch between 8kw loads?

The customer I have (a Deli) wants to add a 8kw pizza oven but only has a single phase supply and is already at capacity at 80 amps.

He has a industrial size oven and chicken rotisserie which totals around 8kw which is used during the day and the pizza oven would be used at night. I want a product that would switch between the 2 modes (day and night) and not able to all be turned on at once.

Cheers
 
For dedicated switching between two 8kW appliances, the OP could go 40A CPD to a 40A changeover switch, which will probably be smaller and cheaper. I read this as the one 8kW appliance (be it day or night appliance) plus "everything else" takes the load up to around 80A
 
Good luck with that. Make sure you detail the cert. Pretty likely after you've done they'll find a way to run both together with a nail in the fuse to stop it blowing.
 
a digital time clock and use it to control a contactor,
The contactor would power one or the other,
the time clock sets when that is
easy as !
next problem ?
That's very restrictive - sooner or later they will want to use the pizza oven during the day, encouraging a botch.

The IEC60309 idea could work, however as the load is just north of 32A, you would have to use the much larger 63A variants, which aren't the easiest to couple and uncouple for the layman. Personally I wouldn't be comfortable with someone potentially struggling with connectors in a food prep area with hot equipment closeby.

Either a 40A changeover switch or 3xIEC60309 connectors, plus cabling, assembly and testing will probably be in the region of £200.
 
It really is very simple. A changeover switch is the best thing for the job. Will look neat, professional and is readily available.

I am sure this is a non-issue but usually changeover switches have two supply terminals and one load terminal. In this setup there is one supply and two loads. It may be worth checking technical sheets to ensure they will work as required. As I said I am pretty certain it will be fine but will be worth a check.
 
many moons ago there was a thread about someone having 2 showers but wanted a changeover switch for them so they both can't come on at the same time. Someone posted one.
You could use something similar. Switching high loads.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Leeds

Thread Information

Title
Switching high loads so as not to go over 80 amps.
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
14
Unsolved
--

Advert

Thread statistics

Created
dtec dave,
Last reply from
dtec dave,
Replies
14
Views
1,398

Advert

Back
Top