I'm just wondering if anyone knows of a product that can switch between 8kw loads?

The customer I have (a Deli) wants to add a 8kw pizza oven but only has a single phase supply and is already at capacity at 80 amps.

He has a industrial size oven and chicken rotisserie which totals around 8kw which is used during the day and the pizza oven would be used at night. I want a product that would switch between the 2 modes (day and night) and not able to all be turned on at once.

Cheers
 
For dedicated switching between two 8kW appliances, the OP could go 40A CPD to a 40A changeover switch, which will probably be smaller and cheaper. I read this as the one 8kW appliance (be it day or night appliance) plus "everything else" takes the load up to around 80A
 
a digital time clock and use it to control a contactor,
The contactor would power one or the other,
the time clock sets when that is
easy as !
next problem ?
That's very restrictive - sooner or later they will want to use the pizza oven during the day, encouraging a botch.

The IEC60309 idea could work, however as the load is just north of 32A, you would have to use the much larger 63A variants, which aren't the easiest to couple and uncouple for the layman. Personally I wouldn't be comfortable with someone potentially struggling with connectors in a food prep area with hot equipment closeby.

Either a 40A changeover switch or 3xIEC60309 connectors, plus cabling, assembly and testing will probably be in the region of ÂŁ200.
 
It really is very simple. A changeover switch is the best thing for the job. Will look neat, professional and is readily available.

I am sure this is a non-issue but usually changeover switches have two supply terminals and one load terminal. In this setup there is one supply and two loads. It may be worth checking technical sheets to ensure they will work as required. As I said I am pretty certain it will be fine but will be worth a check.
 
many moons ago there was a thread about someone having 2 showers but wanted a changeover switch for them so they both can't come on at the same time. Someone posted one.
You could use something similar. Switching high loads.
 

Reply to Switching high loads so as not to go over 80 amps. in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
397
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
986
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
Obviously not a building/DIY forum so will keep it short but yes - we've taken all the floors up. Several joists in the bathroom need doing as...
Replies
8
Views
2K
  • Question
What is the distance from the point outside the house to the shed?
Replies
8
Views
789

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top