SY cable on EICR again .... | Page 4 | on ElectriciansForums

Discuss SY cable on EICR again .... in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

The use of SY cable is "discouraged" within BS7671:2018+A2 2022 On Site Guide Section 7.9, as generally it is not manufactured to a British or Harmonized standard.
It is not rated for external use or for use in ducts. It's normally classed as a control cable rather than a power cable.
On an EICR it should be recorded as a non-compliance.
 
I dont understand why it is so popular, i have even seen it used on a 350KVA generator for power.
Its horrible, whenever you touch the screen, which i would only earth one end anyway, its expensive for what it is and there are better cables for all the uses we come across. I think its toughness is an illusion and its outdoor performance is shocking. However, unless it has damage, i would C3 it as there are better products out there, that will last and perform better under most circumstance
 
Depending on the size of the company, ie, has a H&S department or H&S. I'd just use the phrase that's it's not compliant with BS standards and insurance would likely not cover any incident arising from its failure. Whether that 2nd part of the statement is true or not I wouldn't know. But it may start the conversations along the lines if "what if he's correct and we have a fire or death".

My last company with 30,000+ employees would have started a switch out programme on a phrase like that. Quite proactive to be fair to them. One guy cut himself badly stripping a cable with an electricians knife, next week they were banned and a bunch of new bespoke tools appeared that couldn't get you.

Depends on the company you work for I guess. I'd emphasise the poor workmanship items over the construction of the cable in conversation. Like the glanding, poor terminations, etc. and back it up with a mention of the outdoor cable being close to failing being non BS approved.
 

Reply to SY cable on EICR again .... in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
709
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
3K

Similar threads

They do a cy type with pur coating and it is even tougher but is shielded
Replies
3
Views
448
In the 80's I was taught that with PME earthing arrangements we used 16mm for the main earthing conductor, some went a bit crazy and were bonding...
Replies
11
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top