A few points to note:-
SY cable does not comply to British Standards in using it you will have:-
A- understand why it does not comply.
B- document its use and why you believe it is suitable for your installation.
The use of this cable in the industry brought it big concerns and was clearly been used for purposes it was never designed for or was suitable for.
If you have it on or around machinery where it may come into contact with the normal oils, greases, coolants etc used then it should not be used.
If it is subject to possible damage then it should not be chosen in the mindset that it is a armoured flex, it is not it is a screened flex which can afford some kinds of damage a standard flex couldn't but also it is prone to damage where other flexes would be resistant IE UV damage, outer sheath is softer than standard pvc environmental covering and it has low resistance to chemicals and oils.
I conclude this cable should not even be in our industry, it is mi-sold, misused and has forced the regulatory bodies to step it and express its use does not conform to our recognised standards.
I have a pet hate of this cable because of the amount of times I have seen the result of its poor application, I have in 2 decades found several times that damaged cable has made the sheath live and in some cases given uses shocks simply because of misuse and the wrong applications of its use.
I would say if you have routine machine movement for maintenance and cleaning then wire it with a suitable HO7RN-F a cable designed for the purpose of most industrial environments and put it on a plug and socket arrangement so it can be disconnected, I have done this for many decades and never had issues, if you find you are then the operators/employees need educating and taught how to clean and service the machines safely.