PVC is not good against oils, it is well known and is evidenced based, there was major issues in the past with PVC and bitumen based building materials also other insulating or decorative, this somewhat led to a change in the chemical structure of pvc but it still cannot cope with natural or synthetic oils, you can easily tell because it start to become stiff as the oils leach out the natural plasticisers in the pvc.

I design controls for machines and the wiring to boot, I have to use specialised cables to suit too like used in energy track where they are designed for repeated constant movement, I spec'd some of my jobs to give a service life according to the manufacturers details of 10 to 15yrs with flexing in the million+, some of them are still going after 20yrs.

I can tell you from experience that I seen SY used to do the same and it barely makes a yr on frequent flexing and is why it is not designed for it, I can cite you all the info from companies like Lapp or Igus who make these cables and have spent 100,000's designing and proving their products ...

SY is snake oil to the electrical industry, it has been pushed and promoted by non electrically minded sales people to ignorant professionals that it is a wonder solution but like expressed before, it is not recognised by BS standards and is misused so much it is worrying for the industry as a whole.

In such circumstances, could sy cope for 1 year without issues? In a single years use is there a concern about oils and subsequent breakdown?
 
Just to add my 10p

SY (and CY) is a pretty poor cable for EMC compatibility too (VSDs) as the screening is usually extremely poor (full of holes) and it’s impossible to buy it in a concentric formation ie 3 core.

So it’s no good for anything basically but the AC boys cannot get enough of it.
 
In such circumstances, could sy cope for 1 year without issues? In a single years use is there a concern about oils and subsequent breakdown?
When you design a machine and its controls and cabling you sell it on the premise it is of good design and service is minimal and not too costly, in answer to your question then I would need to know the travel, the duty of flexing and the usage of the machine but regardless of this SY is not a cable designed for constant repeated operational flexing, I will provide a link to show you how much tech' goes into energy cables (constant flexing cables)..just an example of many companies out there I use that you don't get at you average wholesalers ...https://www.igus.com/contentData/wpck/pdf/US_en/7 guidelines for continuous flex cables.pdf
 
Just to add my 10p

SY (and CY) is a pretty poor cable for EMC compatibility too (VSDs) as the screening is usually extremely poor (full of holes) and it’s impossible to buy it in a concentric formation ie 3 core.

So it’s no good for anything basically but the AC boys cannot get enough of it.

You are correct for the most of your comment but weirdly some VSD manufactures promote and accept the use of SY cable as a solution, the issue is the quality, most SY has loose wound braiding, the ones they suggest has compact tight braiding ...easy to tell in that it is impossible to unravel the braiding on the good stuff without time and determination although the correct expensive glands should be used anyway.
 
The only time I’ve seen a decent SY braid was on a project in Holland when the customer requested all cabling had to be from LAPP.

Everything I’ve seen from the normal wholesalers has more holes in it than a sieve.

I’m aware some manuals state it can be used but the fact you cannot buy it in 3 core, it’s poor steel braid makes in useless especially on large motors.

I’d rarther (and have) use SWA. But that has its own issues as you cannot terminate that directly into the drive.
 
You can buy it in 3core?
Just a note rode wickerman at alton towers in the summer.... Theyve used it for all the speaker cabling and at thorpe park there was an abundance of it on the ride controlls of swarm
 
The only time I’ve seen a decent SY braid was on a project in Holland when the customer requested all cabling had to be from LAPP.

Everything I’ve seen from the normal wholesalers has more holes in it than a sieve.

I’m aware some manuals state it can be used but the fact you cannot buy it in 3 core, it’s poor steel braid makes in useless especially on large motors.

I’d rarther (and have) use SWA. But that has its own issues as you cannot terminate that directly into the drive.

The thing with SWA is that it is not suitable for EMC screening that drive cables will require.
This is a known issue with SWA & drives, and has been proven with EMC testing and analysis.
 
I installed SY cable in the car factory in the 1980’s. It was used on conveyor systems etc. I know the paint shop install I worked on is still there, wonder if the cable is?
 
Played crazy golf last week and it had been used everywhere on the course which is only a few months old! Chucked in the water features and laying on gravel and all in sunlight, ill give it a couple of years! Its been used everywhere! outside lights etc all in compression glands! Bloody abortion
 
I think there is some confusion here to what classifies as SY cable, SY is a standard pvc flex with an external braid and usually a clear jacket, other cables with a braid are not necessarily SY even if they appear to be, the proper energy cables fitted to most automation plants or many of the machines I service have very similar traits and sometimes appear to be SY but they are specialist cables that you cannot just walk into your wholesalers and pick up off the shelf.
When I buy the correct cabling for repeated flexing joints you are required to do a lengthy check list of all the environmental issues it may be subject to, the bending radii, the number of flexing actions it will undergo etc etc and you are looking at several quid a meter in comparison to a quid a meter for its equivalent SY version, the last stuff I used was from IGUS and came in at about £400+ for 2 x 15m lengths of chainflex cable 4mm 4core and a 15m 7core which is about 5 x the cost of equivalent standard SY and understandably so, it has a 10million flex lifespan and on the job I put it on it will last 10yrs plus (exposed to all outdoor temperatures, direct sunlight etc), If I used normal SY it would fail within a few yrs and end up costing more in replacement and servicing over the same period.

I did have pictures of when standard SY is used in forced flexing conditions and the results are not pretty but cannot find them, I will also put my hands up to its deliberate use myself but only as a stopgap to get a machine running while the correct cable is been shipped in.

If one understands the construction of a energy flex cable and why it is design like that and compare it to your bog standard SY then you will understand why standard SY should never be used, if you see examples in the industry of what appears to be starndard SY used in this nature then I would need to know the manufacturer and the product code to give a suitable response.
 
That has a CPC in the 3 cores spoon. You should not sleeve the CPC and use it for a phase obviously.

Obviously..
I have never done that.
 
Funny...I had to dig out/remove SY cables in a garden previously owned by an electrician...it had part turned black over time and braid was rusty ..not fit for the outdoor life.
 
Funny...I had to dig out/remove SY cables in a garden previously owned by an electrician...it had part turned black over time and braid was rusty ..not fit for the outdoor life.

Maybe he took them from another place where they were not suitable and used them at home as they will do the job, and were free :D
 
I certainly wouldn't recommend it for external installations as I spent a chunk of last year replacing SY .... where it appeared to be UV damaged and outer sheath very brittle and cracked..... not sure on the brand as we did not complete the initial install
 
A client has just purchased a portable heater (Ive not seen yet, only a photo) that was supplied with SY cable.
It was bought from a reputable British company so presumably meets BS!
The trouble is the lead is not quite long enough so have bought a marginally longer cable to replace it with.
I don't have a problem in using SY in this instance but am waiting to see how the manufacturers have earthed the braid. (Industrial 3ph [Commando] style plug to appliance).
 
Used it all the time in the food industry a few years ago. Never had any issues.
Only issues was water ingress into the braid if the clear plastic outer got damaged from wear and tear....

Never used it on site apart from the plant room type scenarios..
 
In most cases damage occurs as a result of poor design or inadequate protection. And the what happens after damage has occurred is also important.

Not really sure where your heading with this, SY has a place along with all other cables, methods etc

You select, design accordingly !
 
It’s being used everywhere,young lads are using it for temp electrics on site,supplies to caravans.
We would never use it always Swa’s..it’s not a BS & discouraged for use in 18th,use it at your own risk assessment & peril
 
Not really sure where your heading with this, SY has a place along with all other cables, methods etc

You select, design accordingly !

I'm not heading anywhere, just sharing my views on the subject.
Yes it has a place, and when it is the best cable for a particular job I will use it. However it is very often used when it is not the most suitable cable for the job, or where it is unsuitable fir the job.
 

Reply to SY Cable? Thoughts? in the Talk Electrician area at ElectriciansForums.net

Similar Threads

  • Question
It’s still not recognised in BS7671… but used all over the place. Seen portable cabins cabled in it… external use prohibited Its probably easier...
Replies
8
Views
3K
Depending on the size of the company, ie, has a H&S department or H&S. I'd just use the phrase that's it's not compliant with BS standards and...
Replies
48
Views
10K
Thanks all for your comments, advice and suggestions. The following is probably pretty boring for most, and is simply a summary of how the job...
Replies
8
Views
489
  • Question
It's ok if you use the correct driver for the application.
Replies
14
Views
2K
loz2754
L
  • Question
Hi Gingerrubix, The fact that your previous Tenant replaced a faulty socket plate which he used for an external EV, raises an eyebrow. Also your...
2
Replies
25
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks