Well , here is an overview from Eland Cables on SY.
It may answer a few of the questions.
SY Cable | Eland Cables

And a manufacturer that says it can be used outdoors if it is protected.
It's all down to researching the product to suit what you need

http://uk.rs-online.com/web/p/sy-cable/0522531/
 
Last edited:
Earthed yes, but it cannot handle fault current so cannot be used to provide any protection such as that provided by SWA, MICC or any bs8436 cable
I see. So what would happen if for example you were to go through the earthed braid with a grinder or a chisel or something, and into the live conductor?
 
I see. So what would happen if for example you were to go through the earthed braid with a grinder or a chisel or something, and into the live conductor?

Subject to a few variables the two likely outcomes are:
1 the braid melts before the ocpd clears the fault
2 the ocpd clears the fault before the braid melts.

Firstly if an rcd is in use then it should clear the fault.
If the fault current is high enough to cause instantaneous operation then scenario 2 is likely.
If the fault current is low enough that the ocpd does not operate instantaneously then situation one could occur.
Both options could easily result in a cloud of vapourised molten metal
 
Also consider most people just use stuffers and peel back a few strands. So Daves option 1 the most likely.
 
Used miles of the stuff back in my days in the car factory, for conveyor systems etc. It was specified then, as it provided more of a durable cable than heavy duty flex. Guess approved practises change over time, probably end up with twin & earth being 'discouraged' in due course.
 
We sometimes use SY for power between the power dist board and other equipment in the installation. Only when SWA is not needed.
I contacted Eland to see what they thought and below is their response: They responded really quickly which is always great and I have ever had a problem with these people.

Themain issue is that YY and SY cables are being applied incorrectly, for exampleYY cables have been installed as a replacement for Twin & Earth, SY cableshave been used in direct burial applications as a replacement for SWA. Theadvice given is that cables used for compliance with BS 7671 need to complywith a published British Standard, or UK adoption of a CENELEC standard. Thiswill depend on the installation.

With regards not using SY and YY cables in fixedapplications , the reasoning behind this is given within the new onsite wiringguide published by IET is that the SY and YY cables have not been made to aspecific standard.

There have been a number of articles published by BASEC, NICEIC and ACIregarding the use of YY, CY and SY cables, the articles identify that thesecables are not included in BS7671 and are therefore could potentially not be fit for purposeas fixed wiring cables, please find below links:
http://www.basec.org.uk/News/BASEC-News/Be-Cautious-of-Midleading-Claims-Associated-with-YY-and-SY-cables
http://www.aci.org.uk/news/aci-issues-warning-installers-over-cable-claims



 
Just because something is not recognised by BS7671 it does not mean you cannot install with it. The cores of this cable, apart from the cpc may well all have black insulation but they are numbered.
 
Last edited:
I would always be selective about where i use SY, last time i used it was for temporary lighting within a semi derelict building. all clipped to the ceiling out of harms way.

And when i used to do the very odd few houses i would use YY to connect cookers to the outlet plates. apart from that dont use the stuff.

Tell a lie, used some YY the other day to flex up a couple of UPS's
 
What made you choose SY for that application? I can't see what advantage it could have over a common rubber sheathed flex in that environment?

And why use YY for a cooker and not a heat resistant flex?
 
The reason for using the SY is that the part derelict building has SWA's, Conduits, T&E running everywhere. so SY stood out like a sore thumb in contrast to all the dead circuits that were still in. and yes i used the correct glands.
 
The reason for using the SY is that the part derelict building has SWA's, Conduits, T&E running everywhere. so SY stood out like a sore thumb in contrast to all the dead circuits that were still in. and yes i used the correct glands.

Interesting, I hadn't thought of that.

I might have used blue or orange flex, but only because I've got a shed load of it gathering dust in stores
 
On a job recently the aircon guys used SY everywhere, at every accessory they had just used stuffing glands. They were not happy bunnies when it come to snagging and I made them change all the stuffing glands for XT/CXT glands with banjos and fly leads where necessary:hurray:
 
On a job recently the aircon guys used SY everywhere, at every accessory they had just used stuffing glands. They were not happy bunnies when it come to snagging and I made them change all the stuffing glands for XT/CXT glands with banjos and fly leads where necessary:hurray:

All the small installations in shops and the like are done like that up here.
 

Reply to SY, CY None Compliant???? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Sticky
  • Article
Wicked I've just actually looked through it and it's very smart. Some good stuff in it. There's a tile association company that do a magazine...
Replies
2
Views
315
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
295
  • Article
Hi everyone, Another weekend, another sale! Get ready for colder days with Haverland Radiators, combining efficiency with modern design. Keep...
Replies
0
Views
361

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top