When changing a domestic CU, I normally replace / upgrade to 25mm tails regardless of the main fuse size.

What do you guys do???, I was talking to a colleague who sticks with 16mm on a 60amp.

Answers on a postcard!!!:)

G
 
Depends on the max demand of the install in general, to be fair considering the average length of the tails ie less than 3 mtrs (a lot less in most cases) chances are your not going to have much of an issue.
If you like to use 25mm tails so be it, but 16mm is often good enough.
That said I use 25mm if upgrading.;)
 
16mm fine if 60 amp in place ;)

if someone comes along later and changes fuse to 100 amp its down to them to change the tails too :rolleyes:
I agree but the DNO are their own entity and they tend not to bother checking tail size when replacing fuses or upgrading cutouts as its on customers side all they bother with is earthing is done. Also the fuse type they fit allows for long duration on smaller overloads but this can exceed the tails tolerances if say 16mm fitted. I would only fit smaller tails if the load downstream is limited by the nature of the mcb's fitted like a 1 or 2 way board with max load of the mcb's cant exceed the cables capacity without the mcb's tripping themselves.
 
think i pay about ÂŁ4.50 plus vat in the wholesalers for the kit. used to have them cut off the reel but got fed up waiting for an hour while the guy wandered off, probably had a cig and a couple of coffees whilst he had us stood there waiting :(
 
I would only fit smaller tails if the load downstream is limited by the nature of the mcb's fitted like a 1 or 2 way board with max load of the mcb's cant exceed the cables capacity without the mcb's tripping themselves.
the op is about a cu chage with existing 16mm tails on a 60 amp fuse

in answer to his question there is no need to upgrade to 25mm as the ccc is fine

if the customer is having extra circuits put in at the same time and it is likely the fuse will be upgraded then put 25`s in

have yet to find a dno that will put a 100 amp fuse in with 16mm tails in place :eek:
 

Reply to Tail size what do you use in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
223
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
683
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
625

Similar threads

Yes the first bit is just standard wiring, TNS lead cable into cut-out, cut-out to meter, meter to DP isolator, top of isolator is sealed as per...
Replies
8
Views
1K
  • Question
With what looks like only 5 circuits you can probably put a little 5 way garage consumer unit in there if money is tight
2
Replies
17
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top