L

LlandrilloSpark

Fellas

Im just writing up the 5 flats I inspected last week, all the service heads/fuses are new to within 3 years, the cut out fuses are all 100A and tails all 16mm, I know discretion is sometimes needed in this area, on some flats the Max demand reaches 90-100A whilst in others 65-75A, would anybody agree that this is basic circuit design and those with the high max demand need the tails changing?

cheers
 
it all depends on whether the actual max. demand is close to the calculated value. technically, you should fit 25mm tails with 100A DNO fuses, but recently i had a site where 16mm was carrying 95-100A for over an hour . highest temperature of the cable was recorded at 40geg.C. well short of it's rated max. of 70.
 
Fellas

Im just writing up the 5 flats I inspected last week, all the service heads/fuses are new to within 3 years, the cut out fuses are all 100A and tails all 16mm, I know discretion is sometimes needed in this area, on some flats the Max demand reaches 90-100A whilst in others 65-75A, would anybody agree that this is basic circuit design and those with the high max demand need the tails changing?

cheers
I would be very surprised if the total load for 5 flats at any given time was more than 150Amps unless they had NSH's.
 
I agree - 25mm 100A 16mm 60A
BUT the NICEIC assessed a job that i had done, (c/u change in an average sized 2 bed house) and she claimed max demand for that house would be 10A!!!!!!!
Her opinion was "ignore lighting (that uses no power) ignore the shower (its not on long enough) take 40% of he cooker & socket circuit & thats our maximum demand"
As i said this was the opinion of the NICEIC assessor - not mine. So if this is the case do we ever neeed 25mm in a normal house. and before you ask - no - i didnt argue with her!
 
For max demand for blocks of flats or blocks of houses, refer to Curve "a" on Figure 3.1, page 24 of the "Commentary on IEE Wiring Regulations 16th Edition", by Paul Cook.
 

Reply to Tail sizes - max demand suggests too small in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
279
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
775
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
783

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top