Hi guys,
I have job on to install a consumer unit, the problem is I'm unsure weather to supply the consumer unit with meter tails or an armoured.
the setup is the meters are outside on the garage wall and the consumer unit is on the other side of the garage fed in 10mm tails currently. The distance from the meter to the CU is abou 5 metres max.
Im going to put a 80amp switch fuse in the garage back to back with the meter, but I'm unsure on what would be best to supply the CU in.
i was either thinking maybe using trunking across garage joists enclosing 25mm tails or would armoured be more suited. The customer is using there own CU which ain't metalclad and the gap to fit the board wouldn't allow an adapt box to be fitted aswell.
so all I'm asking is would the meter tails in trunking be the best method or should I look for an alternative.
any suggestions from experience appreciated.
 
I found this bit of information thanks to Lee posting the BS number.

Extra checks needed for a BS 8436 Cable

When the basic overload relationship (above) is applied, virtually all cables are protected from damage by the fault current. However for BS8436 cables, contractors or designers must either read BS8436 in detail or follow the following advice when installing a BS 8436 cable concealed in a wall or partition.
The following guidance is relevant for 1.0mm, 1.5mm2 and 2.5mm2 cables only.

1. The cables shall only be used in circuits protected by a type B circuit breaker to BS EN 60898 or type B RCBO to BS EN 61009 with a rating not exceeding16A, 20A or 32A for cable sizes 1.0mm2, 1.5mm2 and 2.5mm2 respectively.
In both cases the circuit breaker must be energy limiting class 3.
This is because only these protective devices have a maximum current needed to operate them which does not exceed 80A, 100A and 160A in a time of one second, for cable sizes 1.0mm, 1.5mm and 2.5mm respectively, and the let through energy is such that it will not thermally damage the cable.

2. The prospective earth fault current in the circuit does not exceed 5,000A. (This corresponds to an earth fault loop impedance (ZS) of not less than 0.048 ohms

Still don't see FP in there ;)
 
I suggest that you return to the page and re-read carefully.

Do you mean this bit?

Whilst many fire alarm cables to BS7629-1 employ a thin foil screen which cannot meet the nail penetration test given in BS8436 necessary to prove adequate protection, cables with a more robust screen, the same as used for BS8436 compliant cables, such as FP200Gold or FP PLUS are able to comply with the requirements of the nail penetration test and can be selected for such applications.

Where it clearly says that FP200 gold and FP plus are able to comply!
 
Well, it appears Lee is correct in that FP200 Gold and FP Plus meet the requirements according to that page, no mention of just FP200.




Whilst many fire alarm cables to BS7629-1 employ a thin foil screen which cannot meet the nail penetration test given in BS8436 necessary to prove adequate protection, cables with a more robust screen, the same as used for BS8436 compliant cables, such as FP200Gold or FP PLUS are able to comply with the requirements of the nail penetration test and can be selected for such applications.
 
No, I was thinking more about this bit:
Although one may question the necessity, ELV circuits are not excluded from the clause 522.6 requirements. In order to ensure complete compliance with BS7671, the same consideration needs to be given to all fire alarm cabling including the ELV circuits.
 

Reply to Tails or armoured? in the UK Electrical Forum area at ElectriciansForums.net

Similar threads

This was posted this week, on topic ....... https://niceic.com/newsletter/omission-of-overload-protection/?dm_i=7G1W,7GCE,K4L2A,WHET,1
Replies
8
Views
649
  • Question
IMO Better to do something about those ignoring regulations first! Current system is like having a speed limit but not enforcing anyone without a...
2
Replies
20
Views
2K

Recommended Sponsor News

Quickwire Now Sponsor ElectriciansForums.net

I am sure you will join me in welcoming our newest sponsors of ElectriciansForums.net - Quickwire! They have decided to join us after seeing you guys discussing their products here. Now we have an expert on board that you can chat to @Quickwire-Sam who will be happy to answer your queries!

[ElectriciansForums.net] Quickwire Now Sponsor ElectriciansForums.net


@Quickwire-Sam said "At Quickwire, we're all about speed, safety, and reliability. We're a family-run business, and every Quickwire connector is proudly made right here in the UK, ensuring noticeable quality. In short, Quickwire is the fastest connection method on the market. Whether you're an experienced electrician or a DIY enthusiast, Quickwire makes electrical connections ridiculously quick and easy. We're passionate about blending British craftsmanship with innovation. If you have any questions or if there's any way we can help, please just ask me!"

Exclusive Forum Offer! Free euro 2024 wall chart for first 10 responses!

Hi everyone,

We have 10 exclusive Uheat EURO 2024 Wallcharts to giveaway for Electricians Forum Members! The first 10 people to reply YES to this thread - I will message and get them sent out to you just in time for this years tournament! GO GO GO

PCBWay Now Sponsor ElectriciansForums.net!!

I hope you will all join me in welcoming our newest sponsor to the forum PCBWay! You can contact their friendly people by sending a message to @PCBWay who will be happy to answer your queries.

Welcome to the community and thanks for your sponsorship!

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

PCBWay provides services including PCB Prototype and batch Production, PCB Assembly (SMT), 3D Printing, CNC Machining, PCB Design, Electronics Modules Selling, etc. We are committed to meeting the needs of global makers from different industries in terms of quality, delivery, cost-effectiveness, and any other demanding requests in electronics.

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top