My Opening Post was regarding plugging flexed equipment into the fixed installation and this reg expresses that the regulations regarding overload protection do not extend to 'in my case' the jet wash so the flex does not necessarily have to be increased to 4mm/6mm due the the plug top been increased and the nature of the circuit having a front end 32amp protection ... its often a mistake i see where chapter 43 is extended to portable equipment with plugs on ... i was defining the boundaries with my original question.
To note here manufacturers guidelines will overrule anything suggested here and the only concern you should have is if the equipment has zero overload protection due to the nature of the load and dosn't require it that the S/C protection still meets requirements of any flex left at its original size as the time/curve of the front end device with be longer. This could be an issue with long flexes.