Temporary building supplies again | Page 2 | on ElectriciansForums

Discuss Temporary building supplies again in the UK Electrical Forum area at ElectriciansForums.net

cliffed

-
Arms
Joined
Dec 20, 2009
Messages
2,183
Reaction score
697
Location
Worcester
just wondering how you guys,install temp electrics to portacabins
Seen a lot of installs on sites & at schools where I don’t think it’s correct.
Mainly earthing,& earthing conductors,or am I being over cautious,cheers.
 
Any transportable unit will need an earth electrode installed unless it is under the supervision of 'skilled or instructed person(s)' in which case the PME can be used.

Construction sites also need to comply with Section 704 as well as 717.
The only thing would be if it would be realistic,especially Main Earth bonding,concerning the size of the neutral on a tncs
 
I know this is an old topic but I have a container to install on a farm. I'm also wondering what UV protected flex you peeps use? as this container is going to be portable it's a small cabin with commando socket to socket so I need to make up a flying lead. In the case above would it not be to test and see if it passes the disconnection times etc and it would be suitable?
 
16A commando?

I used 2.5mm artic blue flex when wiring up static caravans.
Oversized possibly where 1.5 would do, but the thicker sheath did offer a little more protection, and just “looked” better.
 
just looking up h07rnf looks like for 32a ill need a 6mm 3c but there is also (H)07RC4N8-F which offers more protection or am i going OTT for a flexible lead?
 
Section 717 mobile or transportable units -
717.52 Wiring systems
717.52.1 Where the supply to the unit is by means of a plug and socket outlet, flexible cables in accordance with H07RN-F (BS EN 50525-2-21), or cables of equivalent design, shall be used for connecting the unit to the supply.
 
Section 717 mobile or transportable units -
717.52 Wiring systems
717.52.1 Where the supply to the unit is by means of a plug and socket outlet, flexible cables in accordance with H07RN-F (BS EN 50525-2-21), or cables of equivalent design, shall be used for connecting the unit to the supply.
Oh, thank you for spending the time to find that for me. so I have a get out of jail free card if I use the cable and they damage it. I'm usually always overly cautious with these things and thinking what if !!
 
I have a get out of jail free card if I use the cable and they damage it.
Really H07RN-F is pretty tough, if you need more intrinsic protection then it is really SWA and that is not suited for anything that moves more than very occasionally.

Keeping the flex out of harm's way is the best plan, so attached to tray or in some duct, maybe an overhead hawser if clearance for vehicles, etc, allows it, etc, if you can. However, many temporary sites have nothing to helps with that and are quite brutal in how they treat cables :(
 

Reply to Temporary building supplies again in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
382
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
963
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
much more information required. Is the supply to the first building a DNO supply or a sub main cable from another building ? if it is a sub main...
Replies
5
Views
957
  • Question
I think there is a little truth in what the guy in the video says, but he makes more out of it than he should. A N-E fault on a circuit protected...
Replies
28
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top