Due to the long length of a distribution circuit I'm installing, the cable csa is 50mm sq.
The earthing arrangement at the origin is TT.
25mm tails at the service are to be connected to a 300ma 100amp time delayed rcd then into a 100amp s/fuse ( fuses rated at 80 amp )
From the s/fuse a 50mm sq 4 core cable is going to be ran to a out building some distance away which is to supply a 4 way 3 phase dis board.
The NICEIC advised me to install a separate TT earthing arrangement at the db end.
The problem is I have to terminate 50mm sq 4 core armoured cable into an rccb. I know I have to keep the armoured insulated from the db earthing system but how am I going to connect the tails?
Are there any rccb's which will take this cable size?
It would be a hell of a lot easier to export the origin TT that way I could terminate to a isolator at the db end.
Cheers
If you do still need to find a suitable termination, pin lugs......
@ E54,
Connect them altogether and improve the overall TT system, using the SWA of your 50mm 4 core cable...
That is what I would have done, for the same reason, but I did not want to contradict the NIC, in case it was for a specific reason they wanted it done this way.
Sod the NIC, ....They do not make the rules, even though they like to THINK they can!! Ring them and ask for specific reasons Why they want to separate a TT system into 2 separate earthing systems, ....i for one would like to know that one!!!
Hi Engineer 54
The load is a 50kw micro generator 70amps/ phase max load, the cable is this size to keep the vault drop within the less than 1% range
There will be four inverters supplied from the sub db.
As for the Nic ,the guy did not give a clear reason about seperating the earths just said do it.
Hi Engineer 54
That's because there isn't a clear reason!! Different if the source supply was PME, but it isn't so don't try separating the TT system, you'll be defeating the very nature of a TT system...
Think what PME stands for exactly...
Protective Multiple Earthing , i know, and yes that is exactly my point!! But by just stating PME on this thread it will confuse the young or inexperienced into thinking along the lines of PME/TNC-S supplies, but that was not really what you (or i) were talking about is it??...lol!!!
Reply to Terminating 50mm tails into rccb? in the Australia area at ElectriciansForums.net
I'm assuming the cable will have to be cleated well to hold it in place anyway, as a stuffing gland ain't going to hold it tight like a SWA gland...
You would treat it as a TT installation.