yeah that looks a good method, but the swa will be on an outgoing circuit, and going into a breaker, not the incomer , sorry. large cable due to lengthy run
In that case it sounds like a horrendous design when taking installation and selectivity into account. I wouldn’t be feeding a distribution circuit that’s over 150 meters away using a mcb as it’s OCPD. I would be looking at either a fused switch, a switch fuse or an MCCB with selectivity being a major factor/consideration in the design.
 
Thought you were going to say 3% which would have explained the 70.0, seriously bad idea selectivity aside already mentioned to try and terminate that size of cable to an mcb.
 
70mm on a 63a breaker. Must be travelling some distance

Edit just seen the distance in the comments. Is 70mm still not overkill?
 