Hi All
Recently joined the forum to ask for some information.
I recently bought a flat to let. I was advised by the letting agent to get the electrics tested, although not a legal requirement. The test was carried out by their electrical contractor. He failed the test due to the fuse board not having an RCD fitted. The fuse board is the original board fitted in 2003 when the flats where built. There has been no mods or circuits added to the system and everything is working as it should. I paid ÂŁ348.00 for the test and the RCD to be installed. I have since been told that the test should not have failed due to the lack of the RCD. Have I been stitched up.
Any comments gratefully recieved

Peter
 
I was thinking more of 314.1:

Every installation shall be divided into circuits, as necessary, to:

(i) avoid danger and inconvienience in the event of a fault.


And

314.2:

Separate circuits shall be provided for parts of the installation which need to be separately controlled, in such a way that those circuits are not affected by the failure of other circuits, and due account shall be taken of the consequences of the operation of any single protective device.
I already quoted 314.2 ("due account shall be taken..."). 314.1 requires the installation to be divided into circuits - this has nothing to do with the RCCB. The overcurrent protective device connected to that circuit is what makes it a separate circuit. (See the definition of "circuit" in Part 2.)
 
There is always exceptions but only lazy electricians put in RCD protection where it is not required in my opinion.
Rubbish. Providing RCD protection to BS1363 socket outlets was forward thinking rather than lazy. Particularly in non-domestic installations there certainly are circumstances where it is advisable to avoid RCD protection where allowable but this certainly isn't an example of that. If non-RCD protected socket outlets were to be incorporated in a non-domestic installation then really I would expect to see a non-standard socket outlet rather than BS1363 outlets. (Incidentally, this is a requirement of the Wiring Rules in the south of Ireland where RCD protection of all socket outlets has been mandatory for decades.)
 
I personally would not even code a single rcd protecting an installation in a domestic setting if I saw it during an eicr.
I know that’s not the issue here but let’s not lose perspective that it’s not the end of the world.

It is a C3 all day long.

If it was acceptable then we would not be bothering with split load CUs or RCBOs. We would just wack an up-front RCD on everything. We don’t do this because it is not to Regs and shoddy.
 
It is a C3 all day long.

If it was acceptable then we would not be bothering with split load CUs or RCBOs. We would just wack an up-front RCD on everything. We don’t do this because it is not to Regs and shoddy.
no it’s poor practice which is why we provide 2 or more in an installation
A C3 implies a safety issue which I personally don’t agree however like most people I view a single main switch rcd as poor practice
 
I personally would not even code a single rcd protecting an installation in a domestic setting if I saw it during an eicr.
I know that’s not the issue here but let’s not lose perspective that it’s not the end of the world.
Likewise, unless I had evidence that it was causing excessive nuisance tripping.
 
We all know what the definition says.
According To the definition, my fridge freezer is a circuit.
You however seem to have misread the definition.
The part where it states: “protected against overcurrent by the same protective device(s)”.
I haven't misread the definition. My point is that an RCCB does not provide overcurrent protection, therefore isn't relevant to a Regulation requiring division of the installation into circuits.
 
Safer than what? Is an RCD protecting cables buried in a wall safer than metallic conduit protecting cables in a wall?
No-one suggested that earthed metallic conduit wasn't better. The reality is that in a domestic installation it's not going to be a cost-effective solution though.

That said, I previously did additions in my property in 6491B in earthed metallic conduit. However, when I replaced the DB a couple of years ago I had to provide RCD protection to everything due to other parts of circuits having buried T&E etc.
 
Is having a single RCD that never gets tested safer than not having any RCD at all?
Is having a single RCD that never gets tested safer than having separate RCBOs that never get tested?
If RCDs are so much safer, why are they no an option for cables above ceilings and below floors?
 

Reply to Test failed due to missing RCD in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
373
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
939
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

L
  • Question
My Understanding is the 6 Months interval is IET Guidance and this wording is incorporated onto the label which is a requirement in 514.12.2 where...
Replies
9
Views
668
I usually put something like this To assess compliance with BS7671 for continued safe operation (5 year periodical inspection)
Replies
8
Views
453

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top