Hi All
Recently joined the forum to ask for some information.
I recently bought a flat to let. I was advised by the letting agent to get the electrics tested, although not a legal requirement. The test was carried out by their electrical contractor. He failed the test due to the fuse board not having an RCD fitted. The fuse board is the original board fitted in 2003 when the flats where built. There has been no mods or circuits added to the system and everything is working as it should. I paid £348.00 for the test and the RCD to be installed. I have since been told that the test should not have failed due to the lack of the RCD. Have I been stitched up.
Any comments gratefully recieved

Peter
 
Whats that got to do with it, exactly?
In the OPs case, before the main switch was changed, the situation was all the instances of no RCD protection warranted no more than code C3s.
By changing the main switch to an RCD, we have a non-compliant Installation, which should not have an EIC issued until the non-compliance’s are rectified.
 
-

The whole idea of a part RCD spilt board, was so that the lights remained on for safety reasons when RCD operated. Then later it was deemed that dual RCD boards would be fitted as standard in domestic properties to increase safety.
Literally, you are going back to the dark ages when only one RCD or ELCB protected the whole installation.
Like many electricians, I don't makes the rules, but have to comply with the minimum standards set out. By all means better them.
Yes, we all know that. What we are trying to do here is deal with a real world situation, where typically, Landlords are very reluctant to do anything at all if it means spending money. Yes, obviously, the BEST solution is an RCBO board, but it's NOT going to happen, is it?? I am not living in the dark ages, with respect. It is a lot of Landlords who are living in them, and you as well if you think most of them give a s**t.
 
I'll ask again:

If the operation of the RCD causing the de-energisation of the entire installation poses a danger then is the installation dangerous in the event of a power cut?

If these dangers exist then why hasn't emergency lighting etc. been fitted to mitigate this incredibly dangerous situation?
 
In the OPs case, before the main switch was changed, the situation was all the instances of no RCD protection warranted no more than code C3s.
In your opinion, perhaps. Had there been an electric shower; bathroom circuits without adequate supplementary bonding or even socket outlets I would have attributed a C2.

I'm sorry but I wouldn't be giving a C3 for non-RCD protected socket outlets - or at least not unless exceptional circumstances in my view justified that approach.
 
-

The whole idea of a part RCD spilt board, was so that the lights remained on for safety reasons when RCD operated. Then later it was deemed that dual RCD boards would be fitted as standard in domestic properties to increase safety.
Literally, you are going back to the dark ages when only one RCD or ELCB protected the whole installation.
Like many electricians, I don't makes the rules, but have to comply with the minimum standards set out. By all means better them.
Yes, we all know that. What we are trying to do here is deal with a real world situation, where typically, Landlords are very reluctant to do anything at all if it means spending money. Yes, obviously, the BEST solution is an RCBO board, but it's NOT going to happen, is it?? I am not living in the dark ages, with respect. It is a lot of Landlords who are living in them, and you as well if you think most of them give a s**t.
In the OPs case, before the main switch was changed, the situation was all the instances of no RCD protection warranted no more than code C3s.
By changing the main switch to an RCD, we have a non-compliant Installation, which should not have an EIC issued until the non-compliance’s are rectified.
In the OPs case, before the main switch was changed, the situation was all the instances of no RCD protection warranted no more than code C3s.
In your opinion.
 
I'll ask again:

If the operation of the RCD causing the de-energisation of the entire installation poses a danger then is the installation dangerous in the event of a power cut?

If these dangers exist then why hasn't emergency lighting etc. been fitted to mitigate this incredibly dangerous situation?
Installing emergency light would help, but it would not make the installation compliant.
 
In your opinion, perhaps. Had there been an electric shower; bathroom circuits without adequate supplementary bonding or even socket outlets I would have attributed a C2.

I'm sorry but I wouldn't be giving a C3 for non-RCD protected socket outlets - or at least not unless exceptional circumstances in my view justified that approach.
That’s up to you.
Personally, I work to BS7671, not my own version.
 
What is the point of issuing a C3 for no RCD protection, when 90% of the general public and 99% of Landlords will completely ignore it? It just individuals opinions that a C3 should have been issued in this case. It is not mine, I operate in the real world not some argumentative interpretation of one that some folks seem to.
 
That’s up to you.
Personally, I work to BS7671, not my own version.
Well I'm glad you ain't doing an EICR on any rental property any of my family might have to use any time soon, that's all I can say. Sometimes matey, I reckon you just like being bloody awkward for the sake of it, just my opinion.
 
BS7671 does stipulate that an installation which complied at the time of it’s design/construction is not necessarily unsafe for continued use.
As such if an installation complied without RCD protection, I would not be working in accordance with BS7671 if I were to say the installation is now unsafe simply because the requirements have changed.
 
What is the point of issuing a C3 for no RCD protection, when 90% of the general public and 99% of Landlords will completely ignore it? It just individuals opinions that a C3 should have been issued in this case. It is not mine, I operate in the real world not some argumentative interpretation of one that some folks seem to.
Strange that it’s my interpretation, when my interpretation is the same as the IET’s, and all the recognised bodies.
That’s all, not just the NICEIC, not just Napit, all of them.
 
Yes, we all know that. What we are trying to do here is deal with a real world situation, where typically, Landlords are very reluctant to do anything at all if it means spending money. Yes, obviously, the BEST solution is an RCBO board, but it's NOT going to happen, is it?? I am not living in the dark ages, with respect. It is a lot of Landlords who are living in them, and you as well if you think most of them give a s**t.

What younare actually saying is that you are willing to lower your standards and cut corners in order to make a few quid.

That right there is a cowboy approach to any trade.
 

Reply to Test failed due to missing RCD in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Sticky
  • Article
Wicked I've just actually looked through it and it's very smart. Some good stuff in it. There's a tile association company that do a magazine...
Replies
2
Views
328
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
306
  • Article
Hi everyone, Another weekend, another sale! Get ready for colder days with Haverland Radiators, combining efficiency with modern design. Keep...
Replies
0
Views
366

Similar threads

L
  • Question
My Understanding is the 6 Months interval is IET Guidance and this wording is incorporated onto the label which is a requirement in 514.12.2 where...
Replies
9
Views
604
I usually put something like this To assess compliance with BS7671 for continued safe operation (5 year periodical inspection)
Replies
8
Views
414

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top