Hi Boys,

Just wondering if you guys could clear something up for me.

When testing a rcbo or rcd I would always test from the end of the circuit, for example a socket on a radial circuit.

However was talking to someone recently who told me they test from the load side of the rcbo or rcd at the db. Just wondering if this is ok to do?

I suppose it would save a bit of time walking back and forth from the db to the circuit under test if you performed the test at the db but not sure if it would be allowed or if the reading would be different from carrying the test out at the end of circuit side.

Thanks in advance.

The object of the exercise is to test the RCD or RCBO so why the hell are you testing the circuit??? :30:
 
The object of the exercise is to test the RCD or RCBO so why the hell are you testing the circuit???

Technically correct but Im just a lazy sod who finds it easier to test at the socket using my plug tester thingy that goes on the end of my cables! Unless of course I get a reading I dont like ......
 
As long as all the loads are removed from the circuit you can test the tripping times OF THE rcd/rcbo at any point of the circuit, as stated its easier to just plug the tester into the most accessible socket to test the RCD/RCBO tripping times but for a lighting circuit it easier to test at the DB
 
As long as all the loads are removed from the circuit you can test the tripping times OF THE rcd/rcbo at any point of the circuit, as stated its easier to just plug the tester into the most accessible socket to test the RCD/RCBO tripping times but for a lighting circuit it easier to test at the DB


Jesus, this is like Pulling Teeth!! Why are you still advising to conduct RCD tests at a socket for?? It's not the correct method and is contrary to manufacturers recommendations!! So WHY do you still want to include the circuit wiring FGS??
 
Jesus, this is like Pulling Teeth!! Why are you still advising to conduct RCD tests at a socket for?? It's not the correct method and is contrary to manufacturers recommendations!! So WHY do you still want to include the circuit wiring FGS??

Forgive them Father for they know not what they do.:innocent:
 
Jesus, this is like Pulling Teeth!! Why are you still advising to conduct RCD tests at a socket for?? It's not the correct method and is contrary to manufacturers recommendations!! So WHY do you still want to include the circuit wiring FGS??

Sorry E54 It appears I am wrong as stated in the GN3 it does say that you should test on the the load side of the RCD with the load Disconnected (not just removed) I guess I have done it this way by being showed incorrectly in the first place and the NIC Inspector getting me to carry out the test this way during inspections. Mind you saying that I have never had any problems testing RCD/RCBOs either way so would I be getting miss leading reading when testing at a socket as opposed to the DB ???
 
Sorry E54 It appears I am wrong as stated in the GN3 it does say that you should test on the the load side of the RCD with the load Disconnected (not just removed) I guess I have done it this way by being showed incorrectly in the first place and the NIC Inspector getting me to carry out the test this way during inspections. Mind you saying that I have never had any problems testing RCD/RCBOs either way so would I be getting miss leading reading when testing at a socket as opposed to the DB ???

There are some folk around here who have forgotten more about this game than a NIC Inspector will ever know.

Take heed! ;)
 
Heehee...

"Put your CU outside in the wooden garden shed." NICEIC Techline, 2014.

Great idea I think.

When the meter reader finds his meter has been "rewired" you can deny all knowledge of it ..... "Pikeys done it guv when they broke in to steal my whiskey still".
 
Last edited by a moderator:
Apart from anything else, surely it's easier to test RCD devices at the CU, rather than at a socket where you need to have to keep going back to the CU to re-set the RCD to enable the next test to be conducted. I can understand maybe using a socket on a circuit you are fault finding on, but that's about it!!
 
Most have the 'Auto' feature, so you plug it in somewhere and press test, then you go back to the CU and repeatedly reset the RCD until all the tests are done, then you go off again to recover the MFT!!! :-)
 
Most have the 'Auto' feature, so you plug it in somewhere and press test, then you go back to the CU and repeatedly reset the RCD until all the tests are done, then you go off again to recover the MFT!!! :-)

By which time the Scouse plumber has had it away.
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined

Thread Information

Title
Testing a rcbo at db or end of circuit?
Prefix
N/A
Forum
Periodic Inspection Reporting & Certification
Start date
Last reply date
Replies
29

Thread Tags

Advert

Thread statistics

Created
beatboaby924y,
Last reply from
Geordie Spark,
Replies
29
Views
13,659

Advert

Back
Top