Hi Boys,
Just wondering if you guys could clear something up for me.
When testing a rcbo or rcd I would always test from the end of the circuit, for example a socket on a radial circuit.
However was talking to someone recently who told me they test from the load side of the rcbo or rcd at the db. Just wondering if this is ok to do?
I suppose it would save a bit of time walking back and forth from the db to the circuit under test if you performed the test at the db but not sure if it would be allowed or if the reading would be different from carrying the test out at the end of circuit side.
Thanks in advance.
The object of the exercise is to test the RCD or RCBO so why the hell are you testing the circuit???
As long as all the loads are removed from the circuit you can test the tripping times OF THE rcd/rcbo at any point of the circuit, as stated its easier to just plug the tester into the most accessible socket to test the RCD/RCBO tripping times but for a lighting circuit it easier to test at the DB
Jesus, this is like Pulling Teeth!! Why are you still advising to conduct RCD tests at a socket for?? It's not the correct method and is contrary to manufacturers recommendations!! So WHY do you still want to include the circuit wiring FGS??
Forgive them Father for they know not what they do.
Jesus, this is like Pulling Teeth!! Why are you still advising to conduct RCD tests at a socket for?? It's not the correct method and is contrary to manufacturers recommendations!! So WHY do you still want to include the circuit wiring FGS??
Sorry E54 It appears I am wrong as stated in the GN3 it does say that you should test on the the load side of the RCD with the load Disconnected (not just removed) I guess I have done it this way by being showed incorrectly in the first place and the NIC Inspector getting me to carry out the test this way during inspections. Mind you saying that I have never had any problems testing RCD/RCBOs either way so would I be getting miss leading reading when testing at a socket as opposed to the DB ???
Heehee...
"Put your CU outside in the wooden garden shed." NICEIC Techline, 2014.
Most have the 'Auto' feature, so you plug it in somewhere and press test, then you go back to the CU and repeatedly reset the RCD until all the tests are done, then you go off again to recover the MFT!!!