Hi,
I'm looking for some advice on the results I got from testing a 1000VA UPS in use in a small business. With the permission of the owner I had switched-off and disconnected the PC it was intended to protect.

Firstly, it passed all tests except the differential leakage test. Is it normal for these devices to leak current via the protective conductor?

Secondly, I got a noticeable shock when I removed the mains plug from the socket and inadvertently touched the pins. Is there a legitimate explanation for this?

Thanks in advance.
 
Not sure about the leakage, but the shock may be a result of the rectified mains smoothing capacitors in a switch mode power supply. Should have discharge resistors but if you unplug and touch fast enough they might not have discharged to a safe voltage.
 
Sounds like a switched mode power supply and a bridge rectifier set up. You will get leakage to earth and a belt from the pins sounds like capacitor discharge.

Be very careful testing these type of items as they don't like insulation resistance tests, refer to the manufacturers guidance for testing.

Also I would recommend testing the batteries to ensure they will do their job when required, they need load testing as a shagged battery may well show good voltage but have no capacity for any load.
 

Reply to Testing an Uninterruptible Power Supply in the Electrical Testing & PAT Testing Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
155
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
520
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
465

Similar threads

  • Question
There could also be a completely unsuitable junction box embedded within the wall and tiled over or just cables in choc blocks in old accessory...
Replies
6
Views
962
After getting my --- kicked by the plumbing twice I was not in the mood for taking prisoners. This time I removed and dismantled the pipework and...
    • Like
    • Funny
Replies
1
Views
693

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top