Hi. Silly Question, as a tester / inspector of an installation. How do i confirm that overload protection is satisfied for an existing circuit, or is it just assumed as long as Coordination (p89 18th Regs) is satisfied and the protective devices is of a EN BS device? Practically, how do i confirm this though? Where do i find 'I2' details for OCPDs?

Thanks

John
 
Yes, fuses are following the same basic idea as MCB.

For rewirable fuses (BS3036) there is a larger margin between the fuse rating and the capacity of the wiring (see reg 433.1.202) but for enclosed fuses like BS88, etc, you treat them as for MCB ratings.

The bigger issue with rewirable fuses is if some muppet has used the wrong wire in the past, sometimes to "stop it blowing" without realising what danger it presents. Table 533.1 (p159 of 18th regs) has the nominal diameters of wire but you would need calipers or similar to check that in practice.
 
For 3036 fuses you apply the correction factor 0.725.
for example a cable Protected by a 15 amp 3036 fuse would need to carry 20 amps , if overload protection was required.
@pc1966 explains it nicely.
 
Last edited:

Reply to Testing and Inspection Over Current Protection in the Electrical Testing & PAT Testing Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
314
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
836
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
943

Similar threads

FFS - popped it apart, found the same issue and thought I'd update... You guys were already there!
2
Replies
21
Views
2K
Well yes obviously, but if the transformer is indoors and your lights are 50m down the garden then it's very easy to need pretty big cables at...
    • Like
2 3
Replies
42
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top