E

eagleeye

I have just finished a rewire in wales. All the circuits tested out ok. but as i have never done a test on a tt system i was a bit confused on the reading for the earth loop impedance tests. The test on all circuits were coming in around the 15 ohm mark as did the Ze. is this correct or have i made a mistake. All main bonding conductors were disconnected with only the earth rod connected
 
You are correct
A reading of 15 ohms for a TT system is an excellent result,considering up to 1667 ohms (30 m/amp)is ok
The wiring regs recomend a reading of under 200 ohms.so you are way within whats required

Remember the Zs figures in the big red book refer to TN systems
 
As said that is a very good result. Round my way most of the results I get on TT systems are 150-175 Ohm range.

You have carried out the test correctly as well from what you have written, the only other way of testing a TT system is with an Earth Electrode Resistance Tester and that will take you a while because of having to install another 2 temp rods to test.

I always carry out the test the same way you have listed above ;)
 

Reply to testing on TT system in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
265
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
756
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
743

Similar threads

  • Question
I think there is a little truth in what the guy in the video says, but he makes more out of it than he should. A N-E fault on a circuit protected...
Replies
28
Views
2K
Also use a tails gland and clamp if available and make sure tails are secured to a wall. The danger here is a live to earth fault in the Consumer Unit
Replies
7
Views
568

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top