OP
kes123
Hi, I am being careful. ok so one probe to earth and one probe to line with the system switched off.
megger set to loop Hi. No reading is given.
megger set to loop Hi. No reading is given.
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss Testing problems need a little help. in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
Mine (1553) requires 3 leads for a soft test and I had heard that the new ones have a two lead soft test.yep. the megger 1700 models are capable of doing a 2 lead soft test, whereas all earlier models was a 3 lead test ( so i am lead to believe, anyway )
Hi, I am being careful. ok so one probe to earth and one probe to line with the system switched off.
megger set to loop Hi. No reading is given.
Hi, I am being careful. ok so one probe to earth and one probe to line with the system switched off.
megger set to loop Hi. No reading is given.
Can we please clarify, when you say the consumer unit is protected by, do you mean the main incommer in the consumer unit is an 100A RCD or is there an RCD between the meter and CU?
Whenever you are testing Ze your whole circuit side of your CU should be off as you've disconnected the main earth for the whole installation! So the only thing that should be live in the CU is the supply side to your main incommer.
Ok now I am really confused. the consumer unit is protected by a 100amp rcd.
I am connecting green probe to earth. the red probe to the rdc should this be the live side of the rdc then not the dead side.
my megger is just flashing 55
I know and it remained unanswered, sorry for trying to help.I asked that in post #13