The reading is yes 2.35 ohms. So if it is so high what could be wrong
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss Testing problems need a little help. in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
if its a TN system, then it's the DNO's problem. if it's TT then 2.35ohms is good.The reading is yes 2.35 ohms. So if it is so high what could be wrong
I know and it remained unanswered, sorry for trying to help.
Hi the system is TNS. i am presuming that
because there are two cables coming in from outside
now the alarm bells are really ringing!!!!!!!!Thanks and I understand what you are saying. I have done and passed a 2392 course but the knowledge soon starts to fade unfortunately.
I will keep reading and i will try to avoid live testing at present unless its done through a socket using the adapter.
And thanks for giving the help that In have got
Can we please clarify, when you say the consumer unit is protected by, do you mean the main incommer in the consumer unit is an 100A RCD or is there an RCD between the meter and CU?
Whenever you are testing Ze your whole circuit side of your CU should be off as you've disconnected the main earth for the whole installation! So the only thing that should be live in the CU is the supply side to your main incommer.
Ok now I am really confused. the consumer unit is protected by a 100amp rcd.
I am connecting green probe to earth. the red probe to the rdc should this be the live side of the rdc then not the dead side.
my megger is just flashing 55
Kes
I admire your determination to carry out these tests
I am sorry to say but after reading the thread, at the moment you do not appear to be completely sure what the readings you are getting mean, or what they are relevant too
You are unsure of the system type and you are live testing at source
These tests can be dangerous if not carried out correctly, as you know
Other testing,such as dead testing, after proving dead, would make you more familiar with the instrument and procedures
You may be wise to curtail the live tests for the time being, concentrate on the testing theory and getting to know your machine
When you feel confident of doing these live tests,arrange a session with an experienced person initially
It will benefit you more than stumbling along for the time being
I intend this advise, not as a put down to you,but with your improvement in testing in mind