What is the difference between Ze and Zs???
As far as i thought i knew Ze is the circuits earth loop impedance and the Zs is the installations incoming loop impedance??Real confused?!?!?!
 
Ze = EFLI up to the installation (usually measured @ consumer unit).

Zs = EFLI up to & including the installation (highest figure will usually be furthest point on circuit.)

Do you know what R1+R2 is? Zs is basically Ze + R1+R2. Zs can be calculated by measuring Ze and adding the value of R1+R2, giving Zs.

It's late and I'm sure someone will be along with a more in-depth post.:p
 
Last edited by a moderator:
Ze is external earth loop impedance that is the service cable and network

Zs is total earth loop impedance ie the sum of Ze + R1 + R2
 
I remember it as:
Ze [External] ie from supply transformer to main intake position.
Zs [System] everything from supply transformer to the furthest point of consumers installation.

May be basic but it works for me!
 

Reply to Testing Question!!! in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
284
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
786
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
804

Similar threads

  • Question
Good point James. It would have been nice if the manual had mentioned which of the leads were being used for what though. It simply shows the LNE...
Replies
7
Views
609
Good thinking - the other side of that is my garage and also where the gas comes in so probably quite a tidy solution if it comes to it!
2
Replies
22
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top