hi all I am currently working as a mate the contractor I'm working for which I shall not name does the following test.
he only measures zs doesn't do continuity r1 r2 he says that there is a good earth return if these results are within those permitted, he takes his ze from his zs to obtain his r1 r2 value,,now I am not saying I am right but shouldn't you prove a earth path exist before you power up to comply with ados ? The only reason I can see he does this is to save time but I'm guessing he is cutting corners views please or is this permitted.
 
The initial verification would be to the equipment you have installed.....ie the CU and associated gear,such as the RCD's......not the existing outgoing circuits.
IMO essential tests on existing unaltered final circuits would not include R1+R2. IR tests and Zs would be essential because of the changed characteristics of the new protective devices.
R1+R2 tests would be advised but not essential and could be noted as a limitation on the EIC if not carried out.

Thank you, perfect answer.
I was not asking to get out of doing an R1+R2 as i was previously accused, anyway:

You say changed characteristics i get the Zs part as you could be going from bs3036 rewireable to 60898's so different Zs's. Where does the IR come in please?

If you don't do R1+R2 then how would you confirm polarity? When polarity is mentioned is it just reverse Neutral and live being referd to or any cables incorrectly wired?
 
hi all I am currently working as a mate the contractor I'm working for which I shall not name does the following test.
he only measures zs doesn't do continuity r1 r2 he says that there is a good earth return if these results are within those permitted, he takes his ze from his zs to obtain his r1 r2 value,,now I am not saying I am right but shouldn't you prove a earth path exist before you power up to comply with ados ? The only reason I can see he does this is to save time but I'm guessing he is cutting corners views please or is this permitted.

Look at it this way, when you pass your driving test you get taught to drive at 30 MPH on back streets, in reality how often does this happen? testing is the same. Thats not to say i'm encouraging cutting corners!
 
The initial verification would be to the equipment you have installed.....ie the CU and associated gear,such as the RCD's......not the existing outgoing circuits.
IMO essential tests on existing unaltered final circuits would not include R1+R2. IR tests and Zs would be essential because of the changed characteristics of the new protective devices.
R1+R2 tests would be advised but not essential and could be noted as a limitation on the EIC if not carried out.

Can anyone please tell me:

You say changed characteristics i get the Zs part as you could be going from bs3036 rewireable to 60898's so different Zs's. Where does the IR come in please?


If you don't do R1+R2 then how would you confirm polarity?
 

Reply to Testing question in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
307
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
830
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
929

Similar threads

I opened up the CU again and the round junction box above and what I found was the blue and brown wires coming in from the wall just above the 15a...
2 3
Replies
33
Views
2K
Duh!!! Just re-read Op's original post, it was converted to a RFC!
Replies
12
Views
687

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top