Make sure though that all the loads are off ie turn the MCBs off, at the CU, that the RCD protects, as you don't want any loads on the test.
Thank you sounds like an easier way of testing sorry guys i was getting confused.
So just to clarify at consumer unit have main switch off and RCDs AND MCBS in the on position then go to double pole switch or pullcord and test from their ?
Errmmm...
Voltage are you getting paid for doing this work? or are you still training....?
I do worry when I read posts like this.
I suggest you get a sparks in that knows what they are doing...sorry to be blunt but you sound well out of your depth mate.
No not getting paid mate im just trying to think of scenarios i might be faced with after im done with my training etc. I would not undertake any work i was not confident in and did not understand. Im new to this as you can see and im just looking for some guidance its quite alot to take in but im doing my best to make sure i have a good understanding of things before hand.
I've applied to the NICEIC so i will see how my inspection goes but ive always said if that goes well i will undertake my level 2 inspection and testing at college so i gain more confidence before i do any work for customers etc.
This is a picture i've taken of my megger and test leads connected to do the RCD test on my mk dual RCD board
ImageShack® - Online Photo and Video Hosting
Obviously i have not put the busbar in yet but u get the drift.
Main switch on MCBs off RCD ON then test load side of RCD line to earth for that particular RCD or like not so clever pointed out if the RCD side you are testing has a circuit using socket outlets then just use the plug on the megger and test at socket outlet.
first test 1/2 then 1 then 180 wave then 5 then 180 wave record two highest results. The 1/2 test should not trip this is a test to gauge how sensitive the RCD might be ?
Then finally test the manual button on the RCD to see if it works.
Looks fine, you do your tests right there on that RCD and the results will apply to the 4 circuits protected by that RCD.
yeah thanks then ill repeat the same test for the second RCD and that will take into account the 3 circuits on that RCD.
Thanks for fast reply volt.
personally, i just plug in to the nearest socket outlet, with loads removed. problem with using probes is breaking a connection when resetting the RCD. it's rare to find a RCD without at least 1 socket circuit on it. ( RCBOs excepted )
Hi,
Sorry to jump in on this one but, something i come accross the other day, old style re-wirable fuse board with a completely separate rcd for the shower, the pull cord switch went in the bathroom so i just replaced it like for like, the rcd was operating mechanically but how would i test it at the shower/pull switch? (I've disconnected it for the time being). Can i just connect the leads at the pull switch? just seems a bit unsafe doing it this way as obviously it's a live test?
Ben
You can do it there or at the the RCD itself. Better at the RCD itself as you won't have to test on a switch which is over head.
test at the CU. it's easier. switch off all MCBs on the RCD you are testing. clip to earth bar, probe to L on load side of RCD. ( mft set to RCDauto ). switch on RCD, press test button on MFT. reset RCD each time it trips. read off and record trip times. enter the higher of each on schedule of test results. press test button on RCD to confirm operation. ramp test if required. done.
Still not sure as it's on re-wireable fuse board, shower circuit doesn't even go through the main fuse board, it's located separately mounted below. I thought rcd was live test?