The other option, although not ideal, is to test and record that Ze was taken with parallel paths in place. This happens more so in commercial and industrial settings where the supply cannot be shutdown for financial reasons.

That is not Ze, that is a Zs measurement.
[automerge]1592940600[/automerge]
That's what I would have expected to be done. Although would it really be necessary to connect all three of the original wires that now just go back to the cut-out? Surely one would be enough and the other two, now redundant, wires could be cut back flush.

Every time I have come across this it has dated back to the days when 6mm main bonding was installed so all 3 conductors are 6mm.
Now the conductor from the service cutout to the MET should be 16mm for a PME supply (which this is as per the label)
So if they are 6mm then all 3 would need to be connected to achieve the ideal 16mm CSA.
 
either by measurement or calculations.
If I remember from my college course many moons ago, you can also request the Ze figure from your local, friendly and ever helpful electricity supplier.
I've never tried it though. Anybody else had success with this?
 
If I remember from my college course many moons ago, you can also request the Ze figure from your local, friendly and ever helpful electricity supplier.
I've never tried it though. Anybody else had success with this?

They will give you their nominal design limits, which are usually also available from their websites (buried somewhere, if you look hard enough)
For example 100A TNS will normally be quoted as 0.8ohm
100A TNCS will normally be quoted as 0.35ohm for existing supplies or 0.25ohm for new supplies (this is true for UKPN at least, not sure if the others work to 0.25 now/yet)
 
Yes. Those (IIRC ) are the standard figures from DNO Engineering Recommendation P23/1 - which, I believe, is the origin of the 0.35 and 0.8 figures.
 
Remove the small circular plastic inserts you see and undo the screws with the T-Bar @7029 dave has illustrated. While you are at it, remove the bonding cables and insert them into an MET bar screwed somewhere convenient. Really speaking those bonds should never have been put in the DNO equipment but on a separate MET where the main earth is terminated.
 
Last edited:

Reply to Testing Ze when you cannot disconnect the bonding? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
439
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
It’s quite common for an electrician to criticise another’s work as you will rarely get everything perfect.
2
Replies
20
Views
1K
If the shared neutral is lost ,won`t you be getting 400v across both cottages? 2 phase US style but double the Voltage.
Replies
22
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top