davesparks
The other option, although not ideal, is to test and record that Ze was taken with parallel paths in place. This happens more so in commercial and industrial settings where the supply cannot be shutdown for financial reasons.
That is not Ze, that is a Zs measurement.
[automerge]1592940600[/automerge]
That's what I would have expected to be done. Although would it really be necessary to connect all three of the original wires that now just go back to the cut-out? Surely one would be enough and the other two, now redundant, wires could be cut back flush.
Every time I have come across this it has dated back to the days when 6mm main bonding was installed so all 3 conductors are 6mm.
Now the conductor from the service cutout to the MET should be 16mm for a PME supply (which this is as per the label)
So if they are 6mm then all 3 would need to be connected to achieve the ideal 16mm CSA.