new boy21

Hi lads trying to get my head around testing, on insulation resistance testing does a reading of

500 meg and below need to be rewired
 
But under 2meg ohm needs investigation or think nic say under 5meg ohm needs investigating but over 1meg ohm is a pass cheers
 
Despite what the NIC says tracking down and rectifying 'low' readings of 1meg plus is very difficult. It is not always viable to trace and improve readings as high as this,in practice only much lower readings are likely to be a practical proposition to trace......IMHO attempting to improve readings of 1meg plus is pointless....and anything approaching 2megs??...well despite what the NIC may suggest i'ts a waste of valuable time.....5megs???? give me strength.
I realise the increasing use of RCD's makes high IR readings desirable but you can go too far.

Edit....talking existing installations here.....a new installation would expect readings way above the minimum.
 
Last edited by a moderator:

Reply to testing in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
279
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
776
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
787

Similar threads

I was at the other end of the results spectrum today. As I was driving home I had a call from my "Mrs Richards from Fawlty Towers" lady, very deaf...
2
Replies
20
Views
1K
Having some issues with my companys fluke 1662/1663 tester. Zeroing 2 leads for continuity test we get the value 0.08 which is expected. The issue...
Replies
0
Views
254

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top