Fault protection in this case is where such protection (ADS) may not be achieved by a protective device alone.
 
Continuity of a ring final circuit has been tested as part of an initial verification of a new primary school. All the sockets outlets are connected directly to the ring.

The circuit loop length is 58m long wired in 4mm2 live and 1.5mm cod flat profile cable.

The circuit is protected by a 32 A BS EN 60898 type b circuit breaker

The installation has a measured ze of 0.29 ohms

What is the expected as for this circuit?

A. 0 24 ohms
B.0 28 ohms
C.0.53 ohms
D. 0.58 ohms

I've done some calculations but I'm not getting any of those answers which means im doing it wrong.

This is what I have done

Zs = ze + R1 + R2

16.71 x 58 /1000 = 0.96 ohms


O.29ohms + 0.96 ohms

Zs = 1.25 ohms

Obviously that is not right
 
You have done it as a radial circuit not a ring final.
 
Have a look through, compare against yours and see where you may have gone wrong. Come back and tell us once you've figured it out (where you went wrong, not the answer)
 

Attachments

  • 16153138044091565923349493321913.jpg
    16153138044091565923349493321913.jpg
    302.6 KB · Views: 36
Remember when the ring final is connected your resistance is halved due to double csa but the distance is effectively halved.
 
Nice one @Lister1987

Pen and pad is the way foward for sure

I have to get to bed really as im up early and Ive had a long day with college thrown back into the mix but I'll be cracking straight back on with this tommorow.

Cheers for going to the trouble of writing that out

And also to @westward10 for much the same reasons
 
Nice one @Lister1987

Pen and pad is the way foward for sure

I have to get to bed really as im up early and Ive had a long day with college thrown back into the mix but I'll be cracking straight back on with this tommorow.

Cheers for going to the trouble of writing that out

And also to @westward10 for much the same reasons
Just remember to be methodical, helps to give sources too; Table G1 for R1+R2 values, Table G2 for the multiplier etc, it helps it get enground in the mind.
 
I'll be cracking straight on with this after work and something to eat.


My plan was to spend all day sat and sun on revision as well as the remainder of this week but I've just been put on call for my new Job starting Friday. You couldn't write it. I bet it's one of them weekends.
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Camberley
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Trainee Electrician

Thread Information

Title
The measured value of loop Impedance for a circuit is 2.4 Ohms
Prefix
N/A
Forum
Electrical Course Trainees Only
Start date
Last reply date
Replies
34

Advert

Thread statistics

Created
Rather be Fishing,
Last reply from
Rather be Fishing,
Replies
34
Views
642

Advert

Back
Top