B

Bessie

My customer's house has two consumer units connected in parallel. The first one supplies several ring circuits and already had an RCD. The second supplies several lighting circuits, washing machine, microwave, boiler and immersion heater - until I upgraded it, there was no RCD, just a 100A switch.

I checked insulation resistance on both boards before fitting the RCD - all circuits tested out OK, although one circuit on the board with the new RCD was a tiny bit under 2MOhm. Also tested the new RCD, likewise OK. I thought the job was done however customer rang the next day to say the new RCD keeps tripping.

Sure enough, half the times he turns on the microwave the RCD trips. Fair enough, maybe the RCD is faulty after all and a bit over sensitive, but what I can't understand is that when he boils the kettle on the kitchen ring circuit (remember, this circuit is connected to the other board via its own RCD) the new RCD trips even though it doesn't protect this circuit and belongs in a different board!

Is this a recognised phenomenon? Does anyone now what is going on here?

Thanks.
 
Try an IR test from neutral on one board to earth on the other board and vice versa when they are both isolated.
Running a high current item that trips an unrelated RCD tends to indicate a fault on one of the circuits the RCD protects and the high current is passing enough through the fault to trip the RCD.
 
A cct fault is likely. If nothing found then perhaps a hunt through the affected ccts to secure no borrowed or crossed neutrals (result of some diy?). No problem till RCD installed. Just a thought. Cheers.
 
Try an IR test from neutral on one board to earth on the other board and vice versa when they are both isolated.
Running a high current item that trips an unrelated RCD tends to indicate a fault on one of the circuits the RCD protects and the high current is passing enough through the fault to trip the RCD.
Thank you Richard and everybody who posted advice - it all helped! After reading your comments, the solution was quite obvious - I had forgotten to mention that, before I could install the RCD, I had had to bypass one of the original lighting circuits which had an earth-neutral short in the supply cable. I had disconnected the live feed at the CU but left the earth and neutral still attached, so current still leaking from neutral to earth - I just disconnected them at the CU. As you pointed out, it just seemed to be the high current devices on any circuit which caused the RCD to trip - lighting circuits weren't a problem.
 

Reply to The Wrong Rcd Keeps Tripping! in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
271
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
767
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
774

Similar threads

Seen this where T&E has been fixed with a flat bend of too tight a radius.
2 3
Replies
35
Views
1K
Ok I’ll try this when I’m down
Replies
4
Views
382

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top