Boiler panel controlling a 3 phase grundfos pump. Pump was tripping thermal overload...
Pump replaced for a single phase grundfos by engineer etc...
I was asked to convert the control circuit to single phase which I did.
But still tripping on the thermal overload.
Set it slightly higher for now but anyone have any experience when converting etc... Also the original 3 phase pump may have been fine and the issue may have been the contactor thermal overload.
Cheers
 
Some overloads such as the Allen Bradley electronic ones still wont work even with the live looped round and neutral through, they only work with a balanced 3 phase load across the overload. But it's most likely Robs solution will do the job.
 
Ye I did think that but the single phase pump will require a higher start up current as only working through 1 phase.
Will doing this definitely balance it or maybe need a higher rated overload.
The original problem seams it was the thermal overload possible fatigue.
 
Three phase overload relays are designed to protect a three phase motor against single phasing and thermal overload.
Single phasing condition occurs if one of the phases is lost i.e. broken cable/lost phase leaving the motor running on two phases, the thermal overload sees this as an imbalance and consequently trips.
A thermal overload is when the motor draws more current than the rated full load current i.e. the motor is overloaded. Most modern thermal overloads should be set at the rated full load current of the motor for protection purposes.
If you use a three phase overload on a single phase motor you have to ensure all three thermal elements are connected in series, otherwise the overload will trip out on single phasing protection.
The rating of the overload should ideally be selected such that the full load current of the motor falls ideally half way within its range. i.e. Motor full load current 10A, overload range 8 to 12A, relay set at 10A
Most thermal overloads will quite happily withstand 6 or 7 times rated motor full load current for up to about 10 seconds (DOL starting).
 
All motor starter overloads be they electronic or thermal have single phasing protection its a requirement of BS EN 60947-4-1
 

Reply to Thermal overload 3 phase to single phase pump in the Talk Electrician area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
284
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
783
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
800

Similar threads

Some year back there was a case of a young girl killed by being sucked down to the bottom of a pool when being emptied through the power drain...
2
Replies
23
Views
1K
Adding a led strip isn't going to make much difference to the 3 phase balance. No real difference to where a 3 phase machine uses one phase to...
Replies
2
Views
313

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top