The thermo dynamic panels only require small amounts of heat to operate, the heat comes from the compressor to warm the water, not the panel.
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss Thermo dynamics for hot water that runs off atmosphere in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net
the compressor doesn't create heat*, it merely concentrates it from a lower grade to a higher grade of heat. The original heat energy input that allows for the high COP's comes from the panels extracting heat / energy from the air and solar radiation.The thermo dynamic panels only require small amounts of heat to operate, the heat comes from the compressor to warm the water, not the panel.
basic laws of thermodynamics say you're wrong.not if your using gas it dont
I'm fairly obviously not saying that the compressor doesn't extract the heat energy and boost it up to the required temperature, but you seem to be denying that the heat energy actually has to originate in the panel, which is obviously wrong.The panels wont reach 55 degrees if the outside temp at night is -5. Thats why ASHP can work down to -20,
Absorbed Power 0,9 - 1,8 kW ; Thermal Power 3,6 - 7,3 kW
it's not a matter of degrees as such, it's a matter of total energy input into the system. and yes you could put the panel in a lake if you had one, but this is an alternative for those of us who don't have sufficient lakes or ground for a GSHP / WSHP to be an option.Yes but only a few degrees, stick the panel in the ground or lake it would still work, how do you think fridges work or cold stores, freezes.
I have installed a few of these systems and these are the facts:
Ambient air temp - 6 deg C
Water entering temp - 8 deg C
200l of water 8 deg to 55 deg = 2 hours
amp draw = 9amps
Now i'm no mathematician, but what does this calculate into?
Steve
200l at a little under 50deg temp rise needs around 11kWh of energy input.
9amps x 230 v = 2kW x 2 hours = 4kWh
COP = 11 / 4 = 2.75
a COP of 2.75 at 6 deg c ambient air temperature is reasonable, but not particularly impressive for a heat pump tbh, though it at least demonstrates that it's considerably better than an immersion heater, and maybe just about on a par with a condensing gas boiler.
So possibly worth it for those on full electric heating.
electrical input 390 - 550Wpower output 1690 - 2900W
anti legionella heater 1200W
the worrying thing to me about this conversation is that both of you install heatpumps, and I don't yet.
assuming you were using the energie system
have a read through Jason's posts and your recent post then, and the answer should be obvious. You don't seem to be understanding, or at least you're not describing very well where the actual energy input originates in these systems, or allocating any importance to it.Why? I am an air conditioning engineer and have been installing "heat pumps" for 25 years>
yes, this is where the actual additional energy input into the entire system (over the electrical input) comes from, not from the compression / expansion cycle itself. This energy input to the otherwise closed cycle* of the heatpump comes from the panel collecting energy in the form of heat from both the air and the solar radiation, and is directly proportional to the actual heat energy output from the other side of the compressor as is clearly shown in the graph posted.it will now boil/evaporate easily back into a gas using any heat around as long as it is above the gases boiling point of -26 deg C.
fair enough.You have assumed incorrectly, perhaps the ones we installed have a larger compressor and a more efficient heat exchanger.
Steve