There is something odd going on with the day time levels on that graph, as there is potentially 6.4kW solar radiation input to the 4 panels on that system at 1000W/m2, but yet the increased heat output vs no sun ranges from around 2kW at low ambient air temps to 1kW at high ambient air temperatures, so there's obviously something else going on within that system that limits the transfer of solar energy through the system as this is that is the opposite to what would be expected with a normal solar water heating panel.
I think I've now answered my own question.
I'll try to explain...
A is the maximum energy increase from air at -5 deg, assuming all liquid is vapourised. Note, no increase in temperature or pressure of the vapour
B is a rough estimate of the maximum energy increase from and air temperature of 30, and solar input. Note significant increase in both temperature and pressure.
C is the amount of additional pressure required from the compressor to raise the vapour to 55deg from point A
D is the amount of additional pressure required from the compressor to raise the vapour to 55deg from point B
E is the end of the condenser and point where the high pressure fluid passes through the expansion valve
The line at the top between D>C is effectively the additional heat energy output from the heat pump resulting from the additional energy input from the higher air temps and solar.
Now compare that diagram with this one
The top diagram explains (to me at least) why the additional solar input can only result in a relatively minor increase in actual energy output vs the available solar energy to the panels, and why the additional input from the solar decreases as the input from the air increases.
What it also shows though is that there is a significant additional benefit from the solar input though in terms of doing the majority of the work of the compressor by actively pressurising the vapour and raising it's temperature before it enters the comnpressor, resulting in the compressor needing much less energy input.
This explains the high top end COP figure claims for the Energie systems theoretically, which matches with their energy performance figures
Absorbed Power 0,9 - 1,8 kW ; Thermal Power 3,6 - 7,3 kW
The low end absorbed power figure of 0.9kW will be at the highest energy output figure of 7.3kW because much of the compressors work is being done by the additional energy input in the form of solar energy heating the vapour in a closed system and pressurising it.
7.3 / 0.9 = a max COP of 8.1, which actually does look plausible from the diagram above.
* I fully acknowledge that the diagram is very rough and ready, and I don't know what the exact figures are for the working pressures, what temperature the solar input will raise the panel to etc but I hope it works as an illustration of the principle on which these panels operate.