M

MCS Renewables

WPZ in Switzerland have tested a thermodynamic system
test number B-024-12-12

Tested for Energie EST Lda of Lote in Portugal. between 08.08.2012 and 13.08.2012.

It was tested as a domestic hot water heat pump (ie NOT solar thermal)

The test report 250 litre cylinder heated fropm 10.3 to 52.3, a rise of 42C , therefore the COP @ 15degrees C ambient temperature is 1.76.

Being as a decent heat pump can achieve a COP of over 3 at +5 degrees these thermodynamics kits are rubbish and should be used as skip liners.

The cylinders are also not WRAS approved.

Also
1kwhr of gas produces 190 grammes of CO2
1kwhr of elec produces 470 grammes of CO2
1kwhr of LPG produces 230 grammes of CO2
1kwhr of Oil produces 250 grammes of CO2

So unless you are installing in an all electric property these will never qualify for any incentive, ever, and at over ÂŁ6000 for a COP of 1.74 the customers would have been better just burning the immersion heater as they will never get their money back.

The model shown here :- Energie Energia Solar Termodinmica - Products - ECO 200I
claims 390 watts for 150 litres of water so 9.36KW
it takes 1.16 watts per cubic metre x .15 x 50 litres so 8.7KW
So this model has a COP of 0.93 !!!!
And that is using the information from their web site ......

This kit needs leaving in Portugal where it may perform better, up to a COP of 2.73 , which is still poor at 15 degrees compared to most normal heat pumps.
 
I've found some test results listed, and they give it a COP of 2.7 or 3.3 depending on which method is used, with 4.1kWh used to heat a 250l tank to 53 deg.

It unfortunately doesn't say what that starting water temperature was, but a 250l tank is going to take in the region of 12kWh to heat to 53deg from somewhere around 10deg starting temperature.

12:4.1 = a COP of 2.9.

So not the best ever cop, but still not bad for heating water to 53deg.

http://institute.ntb.ch/fileadmin/Institute/IES/pdf/WPZ_Bulletin_01-2012.pdf page 18, Energie Est, lda, Eco 250esm

assuming this is the right kit under test.
 
I wonder how many of these units are fitted legally with full F Gas and unvented Part G also registered with building control as is a required
 
All the companies who've approached us about this have mentioned the F Gas requirements, and all MCS certified SWH companies would already have to have their unvented tickets and be registered with a CPS for building regs compliance.

I suspect there will be a few who're doing it without F Gas, but probably not that many - though it does sound like it's being scam marketed in some parts of the country, so maybe where this is happening.
 
The model shown here :- Energie Energia Solar Termodinmica - Products - ECO 200I
claims 390 watts for 150 litres of water so 9.36KW
it takes 1.16 watts per cubic metre x .15 x 50 litres so 8.7KW
So this model has a COP of 0.93 !!!!
And that is using the information from their web site ......
I've no idea what you're doing with your calculation there, but you've got it wrong - you need to be working in kWh not kW when calculating heat input needed to raise the temperature of a volume of water.

8.7kWh is the energy required to heat 150l of water by 50 degrees, which I assume is what you were saying.

You can't actually get from that figure to the COP figure without knowing both the electrical input wattage, and the time taken to heat the 150l at that wattage of electrical input, and as far as I can see they don't give the time figures.

Assuming their figures are correct though, they give an electrical input range of 390-550 w, and a heat output range of 1690-2900 w.

The COP can be worked out from these figures as being a minimum of (1690/550) = 3.07


Working that backwards from the 8.7kWh heating requirement for 150l heated by 50 degrees, at the worst case of 1690W of heat being supplied, it would take 5.14 hours to heat the tank fully. 550W maximum electrical input x 5.14 hours = 2.83kWh of electrical input for 8.7kWh of heat output, or again a COP of 3.07 using the manufacturers worst case figures.

It's one thing stating that Energie should be supplying proper performance figures for their units at different external air temps, as is required for heat pumps - I'd agree with that, but it's just making the situation worse to start bandying around figures that seem to have been plucked from thin air, and bare no relation to the actual figures that are published, or any sort of understanding of how heat pumps actually work.

- - - Updated - - -

Surely they must be WRAS approved to get in the country and for companies to register them
they have the WRAS logo on their website, so I assume they must be WRAS compliant.
 
You really should go and check that and you won't make the same mistake again.


WRAS is an approval body which is able to verify compliance testing carried out by independent test laboratories. Upon successful verification WRAS are able to grant an approval which demonstrates that a product complies with the water supply (water fittings) Regulations 1999. Compliance with the water supply (water fittings) Regulations 1999 is a mandatory requirement for all products being installed in domestic water systems that may come into contact with potable water, ensuring the products can not affect the quality or taste of the water supply. No products should be installed within the UK that do not comply with these regulations.
 

Reply to Thermodynamic Test results - Not good in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
228
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
689
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
657

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top