Studying the construction of the Magnum heat foil there are Line and Neutral metallic edges running left and right along its length. The heating elements are strips connected between these edges at regular intervals. There is no metallic foil above or below. The N is earth referenced so there is a voltage gradient both between the edges along an element but also to the flooring beneath. Is the polystyrene heat and sound insulating layer in place? This layer would also act to electrically insulate the elements from the flooring which is at local ground potential.

The floor underneath, if it is concrete will have conductance which depends on its chemical make up and moisture content. Wet concrete might have conductivity of 100 OhmMetre whereas very dry concrete 100 MegOhmsMetre. (see : Electrical conductivity - http://www.concrete.org.uk/fingertips-nuggets.asp?cmd=display&id=996)

My pondering is each heating mat will inevitably have a high resistive and capacitive leakage because of the close proximity and large conducting surface area of both the element and floor beneath and above. The polystyrene insulation would reduce these leakage components.

More mats - more leakage current.

I wonder too if there is a best way to lay the mats side by side to minimise leakage current ie:

Is N-L L-N N-L L-N arrangement better than N-L N-L N-L N-L? I have not formed a definite view yet on which is likely to be better but I have a hunch it is the latter.

Time I think to do some earth leakage current measurements to learn more.

Reducing both the maximum potential difference between the mat and the floor and the potential difference to earth across the mat would reduce the earth leakage current. So feeding the mats by a 240V supply galvanically isolated from the mains would reduce the leakage current.

Other than this probably impractical and uneconomic potential 'solution' I reckon it is a question of digging up and re-installing correctly with the polystyrene and metal foil layers.

All academic thinking but maybe of some use to you.
 
Last edited:
I dont like electric UFH at the best of times, when pressured into installing it I always use the warmup brand. The mat in the link looks pretty fragile to me, and I particularly don't like the method of crimping connections to it as shown in the image.
If you have 1M between conductors and a local cpc, then in my opinion its end of story, it needs replacing.
Out of curiosity, what sort of room is this mat installed in?
 
I agree with, it sounds like the mat was damaged during the installation of the floor covering (tiles) and damp has created an earth fault path. If the installer didn't follow the manufacture's instructions and laid the mat incorrectly then its likely any warranty will be void. Some mats are repairable, but looking at the design of the mats I doubt these are repairable. They look very susceptible to damage, a carless tiler could easily nick the mat with their trowel. Especially if it has been incorrectly/poorly laid. I don't see an easy solution to this, to guarantee a fix. Its looking like tiles up and start again at minimum the section where the fault is.
 
A long shot idea - if it's wooden flooring is there a nail through the insulation of a cable at some point along the edge against the skirting board? How to find - IR test to each nail head?
I doubt that, I have never seen a floor layer nail a wooden floor yet.glued and knocked in to position
if he did nail it, they call it secret nailing where you can not see the nail.
 

Reply to This has me mystified! in the Electric Underfloor Heating Wiring area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
381
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
959
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Continuity of the suspect cable appears fine all cores, from this I could work out the length of it and it really doesn’t appear looking at the...
Replies
2
Views
349
  • Question
It is actually specified in BS7671 that the cpcs must be connected to all other sources of earth.
Replies
9
Views
773

Search Electricans Forums by Tags

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top