Getting well into the workshop today… just the general power and I’ve got issues.
So it’s the white CU I’m testing in the middle.
Top left MEM SW/fuse feeds the cafe, top right feeds the public toilets and in turn, the two holiday cottages.
Bottom left is main sw/fuse “M” turns off everything. And bottom right is busbar chamber that everything feeds off.
Haven’t checked fuse sizes in “M” yet. Cannot isolate white CU without turning off cafe and cottages. Whatever size is in “M” is the OCPD for this white CU. I’ll find out when I can turn off the cottages… there’s guests in just now.
But… from the CU. There’s an rfc with 3 doubles. From this, an unfused spur goes into the shop next door… for another 8 points!
I’ll either suggest fusing down here, or pulling out the spur, extending the cable back to CU and making the shop its own radial circuit.
Workshop and shop also share the lighting circuit. Could do with separating that as well.
Only 4 circuits out of a 5+5 dual rcd board used, so plenty spares.
The 2 RCDs are tripping out at 46 and 62 ms. At x1 I