Octopus
All,
Just got in from fault finding a house with a RCD tripping issue ....... it clear cut which circuit is the problem as its almost a dead short L-E
The issue is more about understanding the installation methods used around 1960 ..... the end to end readings for the live and neutral are around 0.15 so that suggests a very short ring - but the ring serves nearly all the sockets in the older part of the house .....
When looking to split the ring, early all the sockets are either 1 cable or 1 old cable and 1 newer cable (and then a socket with the newer cable is close by) which suggests that I'm going to have to start lifting floorboards.........
So my question is was there any "standard" way of achieving such a circuit ... which would make locating the junction boxes easier?
I think I can spot all the "original" sockets as they are just above the skirting board ......
There was 1 point I couldn't access:
This is the immersion switch , on the same circuit, completely covered by the megaflow tank installed about 7 years ago .................. Mr Wet Pants - why didn't you relocate the switch to the right?
Just got in from fault finding a house with a RCD tripping issue ....... it clear cut which circuit is the problem as its almost a dead short L-E
The issue is more about understanding the installation methods used around 1960 ..... the end to end readings for the live and neutral are around 0.15 so that suggests a very short ring - but the ring serves nearly all the sockets in the older part of the house .....
When looking to split the ring, early all the sockets are either 1 cable or 1 old cable and 1 newer cable (and then a socket with the newer cable is close by) which suggests that I'm going to have to start lifting floorboards.........
So my question is was there any "standard" way of achieving such a circuit ... which would make locating the junction boxes easier?
I think I can spot all the "original" sockets as they are just above the skirting board ......
There was 1 point I couldn't access:
This is the immersion switch , on the same circuit, completely covered by the megaflow tank installed about 7 years ago .................. Mr Wet Pants - why didn't you relocate the switch to the right?