I have been asked to look at a consumer unit which is sometimes reading 310V on a meter as read by a plumber who was working on the boiler.

I am going to measure with something better than a multimeter to see what readings are there, but I believe sometimes it does read correctly at 230V.

Thoughts please,
 
Last edited by a moderator:
well first i wouldn't believe a plumber if he said "it'll be dark before morning". tea time usually results in a drop in supply voltage if anything, due to the increased load.
 
Hi there,
I had a similar thing last year,lamps blowing ect,tested volts at a socket and got a
300 plus reading,found nuetrol cable burning on dead side of isolator insibe the cu.
 
I have been to the customers house tonight and got back a short while ago. I did find that the neutral was loose at the incoming side before the meter, not overly loose, but a good 4 to 5 turns on the screw driver.
I went through all the split board and checked for anything that could have been loose. Seems good, just the incoming terminals loose.
She then went on to show me the socket that always trips in her utility room and the shower that always trips. Guess what they did not perform this time haha!

Her spilt board has on the rcd side, two ring circuits, down stairs lights, hmm, and the shower at 45A.

Lights normally not in rcd side right?
Shower correct?
 

Reply to Thoughts on a supply in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Hi everyone, If you are looking for reliable EV chargers, check out our top-rated selection at E2GO! ⚡ Please note that all EV Chargers and...
Replies
0
Views
162
  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
1K
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K

Similar threads

  • Question
Thanks DefyG. I am thinking along those lines insofar as I will ask the electrician to build the DB/CU (plastic if he is OK with that)...
Replies
12
Views
416
Good thinking - the other side of that is my garage and also where the gas comes in so probably quite a tidy solution if it comes to it!
2
Replies
22
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top