Got called out to a hairdressers yesterday after they were receiving shocks from a hair straiteners
Got there to find a single phase consumer unit no RCDs in site and no main earth or bonding at all
So remedy that by putting a temp earth rod in and bonding to water and gas
I have said that it requires a distribution board upgrade and RCDs installed on the shower and socket circuits. As the exsisting consumer unit is a mess
There is a 3phase supply and a 3 phase meter so the customer is being charged for the supply.
They have just lifted the brown phase out of the 3phase isolator and fitted a single phase consumer unit.
Should I keep the supply and quote to install a 3phase distribution board and split the circuits over the 3 phases
Or seeing as the customer isn't using the supply tell them and go down the root of getting the meter changed and upgrading the single phase consumer unit
What would you do ??
The earth rod was a temp fix I already had it on the van and it was just easier and quicker to put the rod in. I am going to contact the energy company to check earthing arrangement and get them to provide an earth for the property if there's one available. Didn't think the energy company would come out within the hour to provide an earth point.
Don't want to put a front end RCD in because you won't get discrimination and limitation of loss of supply.
The old board is a mess I could fit 5 rcbos into the board but at 30 quid a pop it seems a expensive bodge
Think I will go down the 3phase dis board route leaves the 3phase supply and split the circuits over the 3 phases
Thanks for the opinions
Most hairdressing salons get by more than quite adequately with a single phase supply. What i would advise the occupier to do, is get the DNO or provider to change the 3 phase meter for a single phase unit because as sure as eggs are eggs, they are being charged a higher rate standing charge.
If the CU is in that bad a condition, then advise them to change it out with an up to date RCD protected CU. Then it's just waiting to find out if the DNO can provide an earth terminal or not, (you may well have to create a permanent TT earthing arrangement). Whatever happens you'll still need to provide main bonding connection(s) to the MET....
If they only have 5 circuits they don't really need 3 phase depending on load, also they are probably being charged extra standing charges for 3 phases like 3 standing charges
Have you worked out the load that will tell you if you need single or 3 phase, if single get the Supplier to replace saving your customer in standing charges and get them to provide a earthing facility at same time if possible if not go the TT route
Did you do an IR test?......If there is a voltage appearing on equipment there is likely a fault. Putting a (probable) high resistance rod in which wont help ADS without the assistance of an RCD may result in a dangerous situation remaining......after you have attended.
There are 9 circuits altogether in the property but only 5 need RCD coverage
2 showers
3 ring mains
3 internal light circuits
1 outside light circuit.
I tested the earth rod and insulation residence tested the ring circuits no fault found
I then looked at the appliance that they were using and the cable was damaged and hence a live cable was exposed.
I have since removed the appliance from service and also recommended pat testing their appliances as they are all out of date.
So 9 circuits 5 RCD covered ones.
I know they will be paying for a higher tariff because they are being charged for 3 phase.
The loading isn't that high so single phase would suffice, I just didn't know if it was worth the bother of informing the customer and getting the meter changed ect.
I might attempt to speak to the customer and inform them it will be cheaper if they do change to single phase metering.
Thanks for your opinions
Congratulations you have identified a faulty appliance! You may now put a red pat fail sticker on it :D
Oh and you're paying too much for your RCBOs if they are ÂŁ30 each, reasonable SPSN RCBOs can be had for ÂŁ16 each!
I had the same problem on a call out about 5 weeks ago , so I rang Northern power and they were out within 15 minutes and sorted it and that was a Saturday morning!
Reply to Thoughts on distribution board upgrade in the UK Electrical Forum area at ElectriciansForums.net
Has the cover been removed, is it TP bussbar? I fitted one as @oscar21 linked to a few months ago, it was actually a nice board and with the TP...
much more information required. Is the supply to the first building a DNO supply or a sub main cable from another building ? if it is a sub main...