Hi all
Just carried out two EICR in the last two days and found some observations just wandering what others would code them at.
First EICR
6mm twin and earth cable for shower connected in a 45amp bs1361 = code 2
Shower not rcd protected = code 3
2.5mm twin and earth cable running into socket in roof space connected into shower isolator feed from bs1361 45amp = code 2
Down lights for 1[SUP]st[/SUP] floor in loft area sheath of cable short and insulated conductors on show = code
Light in bathroom a pendant and rose = code 3
Also no supplementary bonding to pipe work in bathroom or in airing cupboard = code 2
Secound EICR
No 30ma rcd protection to sockets in stable blokes on TT system feed from bs3036. Only has 100ma main rcd trip at mains would of thought extension leads wuld be plugged in to use outside = code 2
Main earth to earth stake cable clips have weathered and now is loose not supported down wall = code ?
Earth stake hasn’t got a earth inspection box on top so stake is exposed nor a do not disconnect label = code ?
Any thoughts would be appreciated I have looked at the best practise guide issue 3 electrical safety council and code the above.
Just carried out two EICR in the last two days and found some observations just wandering what others would code them at.
First EICR
6mm twin and earth cable for shower connected in a 45amp bs1361 = code 2
Shower not rcd protected = code 3
2.5mm twin and earth cable running into socket in roof space connected into shower isolator feed from bs1361 45amp = code 2
Down lights for 1[SUP]st[/SUP] floor in loft area sheath of cable short and insulated conductors on show = code
Light in bathroom a pendant and rose = code 3
Also no supplementary bonding to pipe work in bathroom or in airing cupboard = code 2
Secound EICR
No 30ma rcd protection to sockets in stable blokes on TT system feed from bs3036. Only has 100ma main rcd trip at mains would of thought extension leads wuld be plugged in to use outside = code 2
Main earth to earth stake cable clips have weathered and now is loose not supported down wall = code ?
Earth stake hasn’t got a earth inspection box on top so stake is exposed nor a do not disconnect label = code ?
Any thoughts would be appreciated I have looked at the best practise guide issue 3 electrical safety council and code the above.