three phase board separation | on ElectriciansForums

Discuss three phase board separation in the Commercial Electrical Advice area at ElectriciansForums.net

Joined
May 12, 2020
Messages
7
Reaction score
1
Location
Nottinghamshire
hello everyone, I have a little problem. I've got a three phase board, it has the three phase sauna, one phase lighting and sockets connected to it. The problem i am facing right now. This is a comercial unit. So the problem is that the sauna makes the RCD trip every so often. And the board is protected by only1 RCD as a main switch. So when RCD trips the whole lighting and other circuits will be disconnected. This is causing a lot of hassle for the customer. And he's wondering if there is anything to do, add additional RCD or do something else without spending a fortune on this.
I have attached a photo so you could better understand what I mean
 
Last edited by a moderator:
And he's wondering if there is anything to do, add additional RCD or do something else without spending a fortune on this

That depends on what the customer considers to be a fortune, some people would consider a £100 solution to be a fortune whilst others would be happy to pay £1k/£1.5k to replace the DB with one which would better suit the requirements.

What does, or does not, actually require RCD protection in this installation?
How many circuits are there in total?
 
I would start by looking into WHY the rcd is tripping.

it would be better to find a potential fault that is developing than find a way to avoid it tripping.
 
I would start by looking into WHY the rcd is tripping.

it would be better to find a potential fault that is developing than find a way to avoid it tripping.
RCD is tripping when people pour too much water on the sauna stones. And that's for protection obviously. So I qas thinking if I could separate sauna circuit and the rest of premises, so if the sauja trips, it wouldn't take the power out in the whole board.
 
RCD is tripping when people pour too much water on the sauna stones. And that's for protection obviously. So I qas thinking if I could separate sauna circuit and the rest of premises, so if the sauja trips, it wouldn't take the power out in the whole board.

Then there is clearly a potentially dangerous fault with the sauna which needs fixing.
 
Is the main board RCD at 30mA type? They are prone to tripping on cookers, etc, with a small amount of damp absorbed by the element so it would not be very surprising if they go on a sauna!
 
Then there is clearly a potentially dangerous fault with the sauna which needs fixing.
Thank you
Is the main board RCD at 30mA type? They are prone to tripping on cookers, etc, with a small amount of damp absorbed by the element so it would not be very surprising if they go on a sauna!
On the RCD it says 100A 3P
 

Attachments

  • [ElectriciansForums.net] three phase board separation
    Screenshot_20200512-153848_Gallery.jpg
    114.3 KB · Views: 16
It's 30mA, if you zoom in a bit you can see it.
OK, that sort of confirms it.

The best suggestion is from @westward10 and as it looks like a Hager board you can probably get RCBO for the single phase circuits easily enough. However, I'm not sure you will find a RCBO to replace the 3-pole MCB in that board (and no space for another pole beside it) so your best/cheapest option might be:

  1. Replace the RCD incomer with a switch (4P matches, but 3P might be fine).
  2. Replace the single pole MCBs with RCBOs for all circuits needing that protection (sockets, lights, etc)
  3. Put the RCD incomer from (1) in to a "garage CU" enclosure to provide separate protection for the 3-phase supply to the sauna.
Maybe others will have better ideas?

It might be worth inquiring of the sauna company what sort of RCD protection the recommend, as 30mA might be less than normal for that sot of load (assuming cable route does not require it).
 
Last edited:
OK, that sort of confirms it.

The best suggestion is from @westward10 and as it looks like a Hager board you can probably get RCBO for the single phase circuits easily enough. However, I'm not sure you will find a RCBO to replace the 3-pole MCB in that board (and no space for another pole beside it) so your best/cheapest option might be:

  1. Replace the RCD incomer with a switch (4P matches, but 3P might be fine).
  2. Replace the single pole MCBs with RCBOs for all circuits needing that protection (sockets, lights, etc)
  3. Put the RCD incomer from (1) in to a "garage CU" enclosure to provide separate protection for the 3-phase supply to the sauna.
Maybe others will have better ideas?

It might be worth inquiring of the sauna company what sort of RCD protection the recommend, as 30mA might be less than normal for that sot of load (assuming cable route does not require it).
Thank you very much for your answers. That helps a lot to understand which is the best option. And if anyone else has any other options i would like to hear them please.
 
This is what you need to replace the rcd switch.
So I have to replace all mcb's to rcbo's and replace rcd to this switch? What about the 3P mcb?
 

Reply to three phase board separation in the Commercial Electrical Advice area at ElectriciansForums.net

News and Offers from Sponsors

  • Sticky
  • Article
Wicked I've just actually looked through it and it's very smart. Some good stuff in it. There's a tile association company that do a magazine...
Replies
2
Views
278
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
270
  • Article
Hi everyone, Another weekend, another sale! Get ready for colder days with Haverland Radiators, combining efficiency with modern design. Keep...
Replies
0
Views
351

Similar threads

Has the cover been removed, is it TP bussbar? I fitted one as @oscar21 linked to a few months ago, it was actually a nice board and with the TP...
Replies
5
Views
534
Sooo the client has accepted that we don't want to be fraudulently taking electricity so that worry is out of the picture. But now basically the...
Replies
32
Views
5K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top