Hi

I popped round to quote for ‘ finishing ‘ a solar install started by a company rhyming with Bird of Polar . The house has a three phase supply, but it looks like someone has taken the three live tails into board not designed for three phase (albeit with a three pole switch).
They’ve only got one phase to the house on a 63A breaker, the house (very large detached property ) demand looks like it would be much more than that. In fact they have a consumer unit with 24 ways inside including a 7kW EV charger, large electric hob and heat pumps
Doesn’t look they have made any effort to balance. And even if I ignore all of that, I would want to use a three phase inverter, and so would want to go to a three phase board.

Am I overthinking this, and this setup is ok, although I’m thinking we need to put in a three phase panel, and then also consider how we provide ongoing supply to main house DB (and summer house)

I suspect that whatever I say is not going to go down well with client, as they’ve already paid some £11k to the now defunct solar company, and all they have done is put solar panels (18x 440W) on roof.

The board was apparently put in by builders electrician.

[ElectriciansForums.net] Three phase supply into single phase board
 
All looks a bit out of kilter I think it should be a double pole switch judging by the Main Switch label with the space to the right if a double pole were fitted for the SPD.
 
But still looks they have almost all the load on one phase
Agreed but difficult with just 4 different single phase circuits but looks like phases are loaded L1 = 16A, L2 = 50A and L3 73A The 10A circuit could go onto L1 to help balance but not a great deal.
 

Reply to Three phase supply into single phase board in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
706
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
3K

Similar threads

I really can't see a problem with it assuming there is a neutral there.
Replies
6
Views
773
  • Question
Probably a bit late for the OP, but there's a very easy option if a manual solution is OK. Rotary cam switches are just the ticket - but not the...
Replies
4
Views
746

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top