there's no way he's got a Ze of 0.18 on a TT system. someone's telling porkies.either that or his pi$$ is marketable.

It is possible , I have personally seen it on an ex military site that we look after and is now a farm . I can not remember the exact Ra now as it was a few years ago , but I have posted about it before ( I can only go back as far as the date of my user name change , for some reason ) in a post about a 100 Ma time delayed RCD going out before the 30Ma RCD down stream , and it was because of the exceptionally low Ra at source .
 
I can't understand why people do not believe what's written in BS7671. If its a TT system with a Ze of 0.18 Ohms after the MPB have been disconnected then 411.5.2 (ii) is sufficient. We used to work to that all the time 20 odd years ago.

However, I've never seen a TT system as low as that. Maybe 0.5 - 1.5 Ohms.

Maybe so , but for the price of them I would rather err on the side of caution and have it as a secondary safety net anyway . No matter what others will no doubt preach , I have seen more than enough Ra's rise and fall , ( Not just the twigs ) far more than I would like to see .
 
I agree with all here, that an Ra of 0.18 ohm on a typical domestic TT system is going to be extremely hard to believe!! lol!! You'd have to be driving a deep rod into a salt marsh to stand any chance of seeing that sort of value!!

As for the Very low Ra on an ex military site, that i can believe, there are probably multiple linked deep driven rod positions around the site, or a full dedicated earth field in place...

On the majority of standard domestic, small/medium commercial systems it is Always prudent to provide the extra back-up protection of an up-front 100/300mA S type RCD device. No-way would i rely on a single RCD device as my sole means of earth fault protection. They are just not that reliable!!
 

Reply to time delay RCD in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
146
  • Sticky
  • Article
Thank you for getting in touch! Looking forward to use your services in the future! :)
Replies
3
Views
484
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
420

Similar threads

I would probably C3 it, based on no contact with sharp edges, all the terminations being tight, and no signs of any thermal damage. With all...
Replies
2
Views
941
  • Question
Good point, I was assuming an up-front RCD is for fault protection within DB, etc, and to cover for a failed RCBO for fault conditions, not as...
Replies
6
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top