A time delayed RCD should always be used if other RCD's / RCBO's are connected after them.

This will allow the other RCD's to operate before triggering the time delayed RCD.
These are generally used in TT installations as the main switch when 30mA RCD's are also used for socket outlet circuits.
 
Last edited by a moderator:
As Adam has stated, S type RCD's will always be required for reliable discrimination with downstream RCD's/RCBO's. The other recommendation is that the upstream RCD device be at least 3 times that of the downstream, well let me tell you now, that rarely if ever works!! Time delay is the ONLY means of achieving discrimination between RCD devices!!
 
Guys, at the risk of going a bit of topic can I expand the question a bit?

What if you are fitting a 100mA RCD to protect a TT installation where there are no other RCDs currently fitted to any circuits? Would you....
a) use a non time delay RCD because they are cheaper and you don't have any other RCDs to require discrimination or
b) use a time delay so upgrades to circuits in the future can be done by adding 30mA RCDs without causing a discrimination problem

This is actually a situation I am quoting for at the moment. Customer doesn't want the cost of a CU upgrade (which I have recommended to give 30mA on sockets, bathroom etc etc) but currently has no RCDs and a Ze of about 50 ohms which I have told him isn't giving him any fault protection.
btw. for what it is worth I have gone for option b).
 
Well use a S Type delayed as the main switch, that's a saving on a main switch, and a 30 Ma RCD on those circuits that require it, which without knowing the job is all of them possibly, I don't want to come across as critical your not insisting on RCD protection on a CU change ? and don't forget also the enclosures type needs to be a class 2 or all insulated for TT's as I interpret the regs
ATB J
 
Well use a S Type delayed as the main switch, that's a saving on a main switch, and a 30 Ma RCD on those circuits that require it, which without knowing the job is all of them possibly, I don't want to come across as critical your not insisting on RCD protection on a CU change ? and don't forget also the enclosures type needs to be a class 2 or all insulated for TT's as I interpret the regs
ATB J

I think you misunderstood me. I was not quoting for a CU change. The work asked for was an outside socket off another, RCD protected, CU. I just noticed that the main CU supplying most of the house circuits didn't have any RCD protection and told the guy that wasn't clever. Not suprisingly the guy doesn't want a ÂŁ100 job turning into a ÂŁ500 job with CU change so wants the minimum that will give him some protection. That would be an up front 100mA RCD without touching the main CU.
 
I think you misunderstood me. I was not quoting for a CU change. The work asked for was an outside socket off another, RCD protected, CU. I just noticed that the main CU supplying most of the house circuits didn't have any RCD protection and told the guy that wasn't clever. Not suprisingly the guy doesn't want a ÂŁ100 job turning into a ÂŁ500 job with CU change so wants the minimum that will give him some protection. That would be an up front 100mA RCD without touching the main CU.

Sorry dude got wrong end of stick, just note it on the minor works to cover your ---

ATB J
 
If you are installing a socket-outlet to be used for mobile equipment outdoors, then the socket-outlet will require 30mA RCD protection.
The problem you have with installing a time delayed up front RCD, is what delay you will use.
1s for distribution circuits, or 0.2s for final circuits?
 

Reply to time delay rcds in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
285
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
787
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
810

Similar threads

Also use a tails gland and clamp if available and make sure tails are secured to a wall. The danger here is a live to earth fault in the Consumer Unit
Replies
7
Views
569
  • Question
much more information required. Is the supply to the first building a DNO supply or a sub main cable from another building ? if it is a sub main...
Replies
5
Views
947

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top