Does anyone know the max trip time for a 100mA time delayed RCD
Quick question
Does anyone know the max trip time for a 100mA time delayed RCD
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss Time delayed 100mA RCD in the UK Electrical Forum area at ElectriciansForums.net
Max 500ms min 130msHi guys
Quick question
Does anyone know the max trip time for a 100mA time delayed RCD
If it is only a 1 second disconnect time required then it will comply as it will trip with in 0.443 of a second.Spinlondon has described the maximum tripping times for circuits that are protected by ADS with an RCD. The circuits would also need overcurrent protection.
Ian1981 has described the trip times for the RCD as a item in its own right irrespective of its circuit connections.
Your trip time of 443ms would meet the requirements for the device as an RCD but would not meet the requirements for disconnection time for a final circuit on a TT system.
Yes, it will comply for distribution circuits (1s), for which it appears to be being used, but not for final circuits (0.2s).If it is only a 1 second disconnect time required then it will comply as it will trip with in 0.443 of a second.
Sorry you said fiIf it is only a 1 second disconnect time required then it will comply as it will trip with in 0.443 of a second.
If it's a metal consumer unit the 100mA will protect the internal link tails incase they short out to the metal case so will comply as it will be a 1 second disconnection time requiredThe 100mA has being used upfront and a dual RCD board has being fitted with obviously 30mA protection for all final circuits.
The time delay is purely protecting the internal tail links in the metal consumer unit.Hmmm, understand that. I also understand sockets, cables in wall less than 50mm etc etc, require 30mA RCD. I also note the use of 30omA RCD for fire protection, etc. An S Type 100mA has only one use?